Hi all,
2 adjacent terraced houses are being joined into one. The supplier meter cabinet is towards the front of each house and the consumer units are over the rear door in both instances. The heating system is oil and there is no storage electric or heat pumps in either unit, therefore, it is likely both houses are 12kVA supplies with 16mm2 mains tails. The houses were built in 2002. The final house would have only 1 no. cooker with oil heating and so a 12kVa supply should suffice for the final two units combined,

It is proposed that 1 of the supplier meters would be disconnected and the associated consumer unit would be connected with a new 16 mm2 SWA to the other consumer unit. This would serve to minimize the amount of rewiring required,

Question:
1. does the utility (NIE/ESB) have particular requirements for supplies to previously separated houses?
2. Any obvious oversights in the above proposal?

Thank you,
 
Hello. It look like you are not in the UK but in a separated part of Europe where all sorts of different rules and regualtions may apply.
Don't you have an electricians' forum in your country?
You might try messaging @Risteard
He lives in the UK but knows a little about your part of the World.
 
Hi all,
2 adjacent terraced houses are being joined into one. The supplier meter cabinet is towards the front of each house and the consumer units are over the rear door in both instances. The heating system is oil and there is no storage electric or heat pumps in either unit, therefore, it is likely both houses are 12kVA supplies with 16mm2 mains tails. The houses were built in 2002. The final house would have only 1 no. cooker with oil heating and so a 12kVa supply should suffice for the final two units combined,

It is proposed that 1 of the supplier meters would be disconnected and the associated consumer unit would be connected with a new 16 mm2 SWA to the other consumer unit. This would serve to minimize the amount of rewiring required,

Question:
1. does the utility (NIE/ESB) have particular requirements for supplies to previously separated houses?
2. Any obvious oversights in the above proposal?

Thank you,
I presume that this job is in the 26-Counties given your location of Tralee in Co. Kerry.

Note that this comes within the remit of Restricted Electrical Works, which can only legally be carried out by a Registered Electrical Contractor (REC) - i.e. a member of RECI (also known under the brand of Safe Electric).

The DSO (ESB) do indeed have many rules as evidenced by the National Code of Practice for Customer Interface (4th Edition). As stated, there is also the law regarding Restricted Electrical Works.

All works must comply with the ETCI National Rules for Electrical Installations (4th Edition) ET101:2008.

You should get a REC on board to design this installation for you and proceed from there.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
tralee

Thread Information

Title
2 houses being joined into one / wiring
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
3
Unsolved
--

Advert

Thread statistics

Created
cobber,
Last reply from
Risteard,
Replies
3
Views
1,022

Advert

Back
Top