B
Becko
Hi Guys,
Two of the jobs I have on at the moment are causing me a bit of a conundrum on how to resolve them, so I thought I'd drop them on here to get your thoughts....
Job 1. I'm moving an 80a 17th edition DB 7m away from suppliers isolator, what size cable, can't find it in the regs? I'm thinking 16mm with separate 16mm CPC.
Job 2. I have 8 floodlights with 1000w lamps in (so 8000w total load). Fed by C50 MCB onto 16mm SWA, dropping down to 6mm at the columns. The impedence readings start off at 0.91ohms and get progressively worse along the 200m run to 1.25ohms. Any suggestions on how to resolve this without digging in a new SWA? RCD at each post maybe?
Two of the jobs I have on at the moment are causing me a bit of a conundrum on how to resolve them, so I thought I'd drop them on here to get your thoughts....
Job 1. I'm moving an 80a 17th edition DB 7m away from suppliers isolator, what size cable, can't find it in the regs? I'm thinking 16mm with separate 16mm CPC.
Job 2. I have 8 floodlights with 1000w lamps in (so 8000w total load). Fed by C50 MCB onto 16mm SWA, dropping down to 6mm at the columns. The impedence readings start off at 0.91ohms and get progressively worse along the 200m run to 1.25ohms. Any suggestions on how to resolve this without digging in a new SWA? RCD at each post maybe?