Looked at a job today and noticed 2 red line cables in one 6amp MCB which was marked up as Lights. The place is a small purpose built flat with a couple of lights in the entrance hall with stairs going up to the living area and the rest of the lights. The two way switch in the hall operates the hall lights in isolation and also the upstairs landing light. The landing light can also be operated by its own switch on the landing. Although the two lines shared the same MCB the Neutrals and CPCs were in seperate slots on the bars in the CU. I thought it would be a simple job to simply disconnect one of the circuits and put it on to the other RCD. This seems sensible given that the flat owner is in her 80s and lives alone and has to come down the stairs to reset the MCB when it trips in darkness. Well I connected one of the circuits to the other side of the board thinking this would solve the issue. I turned on the hall lights and they came on no problem. Ithen turned on the landing light from the downstairs switch and both RCDs tripped. I have put it back the way it was for now and it is working.
Does anybody know why it is doing this and how can I sort it out