looked at a job today. 2 phase and neutral supply, 2 single phase meters.large outbuilding on one phase and house on other
Would it be correct to say that 1 pv systems could be installed on each phase if they are less than 16A?
large south facing roofs for each, no real shade issues and a 1200m2 pond at the bottom of the house to add to the gravy.
i do know that sse charge £250& vat for a network assess visit
Rural property and no other pv i can see in the area
cheers dcf
 
Fronius do a 7kw 2 phase inverter if that's any use - I did ask the question to Fronius as to whether it can cope with split phase and they have confirmed.

At the moment SSE are not charging for a network assessment on multiple installs of <4kW, since July.
 