1. in appendix 4 the volt drop tables.. what is the r , x , z ? how do i incorporate that into the volt drop formula?

2. i have always thought that if you are wiring in singles, the cpc has to be the same csa as line conductors. the designer on this job has spec'd for me to wire rings in 4mm for line and 2.5 for cpc. i looked in the regs could'nt find it but im sure its in there . does anyone what reg it is?
 
Not sure about question 2 hopefully someone else will answer that.

If you look at BRB page 258 top paragraph explains your z r and x

Z cross sectional area
R resistive component
X reactive component

Hope that helps


Chris
 
If you apply the adiabatic equation you may find that your cpc does not need to be the same size as live conductors, otherwise twin & earth cable would not comply with the Regulations.
 
oh right. i was almost sure that you had to use the same size cpc, unless the cpc is incorporated in the cable (ie t and e) oh well thanks anyways. with this r x z malarkey... how do you do the formula? on lesser sized cables it just gives you the mV/A/m figure then you just do that multiplied by the design current , multiplied by the length of run, divided by a thousand.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
2 questions
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
4

Thread Tags

Advert

Thread statistics

Created
joe_berks,
Last reply from
joe_berks,
Replies
4
Views
2,368

Advert

Back
Top