1. in appendix 4 the volt drop tables.. what is the r , x , z ? how do i incorporate that into the volt drop formula?

2. i have always thought that if you are wiring in singles, the cpc has to be the same csa as line conductors. the designer on this job has spec'd for me to wire rings in 4mm for line and 2.5 for cpc. i looked in the regs could'nt find it but im sure its in there . does anyone what reg it is?
 
Not sure about question 2 hopefully someone else will answer that.

If you look at BRB page 258 top paragraph explains your z r and x

Z cross sectional area
R resistive component
X reactive component

Hope that helps


Chris
 
If you apply the adiabatic equation you may find that your cpc does not need to be the same size as live conductors, otherwise twin & earth cable would not comply with the Regulations.
 
oh right. i was almost sure that you had to use the same size cpc, unless the cpc is incorporated in the cable (ie t and e) oh well thanks anyways. with this r x z malarkey... how do you do the formula? on lesser sized cables it just gives you the mV/A/m figure then you just do that multiplied by the design current , multiplied by the length of run, divided by a thousand.
 

Reply to 2 questions in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
559
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
993
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
933

Similar threads

Duh!!! Just re-read Op's original post, it was converted to a RFC!
Replies
12
Views
787
I'd always go for 25mm2 5core over 50mm2 3core, with the cores paired up. Considerably cheaper, easier to terminate and ready to go, if ever 3...
Replies
7
Views
483

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top