Hi guys I was just thinking about what someone put about a question I asked a couple of days ago. I asked about putting an RCD proceted fused spur on a ring main to feed an outside light. they said the RCD fused spur will be fine as long as its not protected by another RCD on the cu. My question is, Can anyone tell me what would happen if it was connected up like this using 2 RCD's ? I cant see it being dangerous or anything but maybe im wrong ?
 
Hi,i posted it.I said it was ok to use the RCD spur as long as the circuit wasn't RCD protected.If the circuit is RCD protected,just use a normal spur.

sorry i know its me being very dumb but what do you mean by "no discrimination between the 2 if they were both 30mA" would they not work ?
They would work,but both RCD's would trip.
 
Last edited by a moderator:
Discrimination(in this case) is having the rcd downstream (fusespur) tripping under fault condition before a rcd upstream trips(fuseboard )if not this would cause nuisance tripping where other items or circuits are lost but it leads to confusion too.
2 rcds are allowed when discrimination is acheived either by having a larger mA rating upstream device or having a time delay rcd upstream if they were rated the same but reg's on tripping times and mA values still need to be achieved in either of these examples.
 
Last edited by a moderator:

Reply to 2 RCD's in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
853

Similar threads

  • Question
I seem to find two types of installation in older houses in which electric showers have been added: those with shower fed from an MCB without RCD...
Replies
9
Views
833
nicebutdim
N
  • Question
ok cheers for the help lads
Replies
7
Views
704

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top