Dear all
Looked a job today in a kitchen
Existing 6mm t&e supply on a 30a Wylex 3036
Lady of the house wants to change existing oven and put in 2 single ovens in one housing
What's the best method of feeding these off the 6mm
Can't do a double socket as it's only rated at 13 / 20 amps
Was thinking of 2 single sockets but I guess it would be a struggle to get 2 x 6mm's into the back of one of them ( or would it )
Advise appreciated please

Ta
 
Dear all
Looked a job today in a kitchen
Existing 6mm t&e supply on a 30a Wylex 3036
Lady of the house wants to change existing oven and put in 2 single ovens in one housing
What's the best method of feeding these off the 6mm
Can't do a double socket as it's only rated at 13 / 20 amps
Was thinking of 2 single sockets but I guess it would be a struggle to get 2 x 6mm's into the back of one of them ( or would it )
Advise appreciated please

Ta
What are the ratings of the 2 single ovens? may need to do some calculations to get the correct size cable, no good bungin 2 ovens on a 6mm if it ain't big enough is it????
 
Thanks for the replies gents
Pete. The ovens are both going to have 13plug tops so 3kw max so 26 amps should be good

Snow. Need isolation as well as cable is just straight out of wall. 50a cooker point feeding the dual appliance outlet seems s but over engineered that's why I thought of 2 single sockets.
 
Go fitting sockets they will need rcd protection, does it already have it ?
Hi westward
Old Wylex board so no RCD as yet. Was thinking of a single RCD external to the board just for this circuit as customer won't go to a board change. Would the dual appliance outlet need to be RCD protected as it's hard wired. I know in an ideal world everything should be but I'm fighting a cost cutter
 
Hi westward
Old Wylex board so no RCD as yet. Was thinking of a single RCD external to the board just for this circuit as customer won't go to a board change. Would the dual appliance outlet need to be RCD protected as it's hard wired. I know in an ideal world everything should be but I'm fighting a cost cutter
Assuming you are not going to chase any more cables in the wall then no, but there is always the good old manufacturers instructions to consider.
 

Reply to 2 single ovens on 6mm T&E 30A rewireable fuse in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
775
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
783

Similar threads

Electric hob/oven range was installed years ago, runs on 2 x B32 MCBs to 'House' (sub)consumer panel, runs to oven on 2 x T&E. Kitchen is being...
Replies
0
Views
288
  • Question
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top