lucus

hi everyone

i have a extension to wire the house has 2 supplies as there used to be a anex attached, if i use the old anex supply for the extension how do i stand on the bonding side of it? the boiler is in the old part of the house and the gas is bonded there, but the sink is in the new part of the house so im planning on bonding this here, has anyone had a simular experiance in the past?

cheers
lucus
 
If the two are completely separate, then you could bond them separately.
If however the heating boiler is in one part, and that feeds radiators etc. in the other, it wpould be best to cross bond them.
 
Are the supplies in the same area of the building? Same supply type (TNS, TNC-S)? Same phase?

Its not the sink that needs bonding its the water mains, so if the 2 parts of the house share the same stop cock then thats what needs bonding.
 
thanks for your reply's
one supply is on front of house and other is on the back where the anex was, they are both tncs and on the same phase. the main water comes in the new extension, should i bond both gas and water from both supplies, its just that getting a cable from the new consumer unit location in the extension to where the gas enters the house (in the exsisting part of the house) will be a right pain.
 

Reply to 2 supplies to house in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
831

Similar threads

Was there any toast to go with the beans? Just joking I think that you ment beams and not beans I am dyslexic and simple mistakes tend to jump out...
Replies
11
Views
1K
Has the cover been removed, is it TP bussbar? I fitted one as @oscar21 linked to a few months ago, it was actually a nice board and with the TP...
Replies
5
Views
612

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top