I have 2 heaters on a 16a radial, but they are running through a 13a fused timer spur. Total measured current drawn is 16.5a, but the timer hasn't popped the fuse so far. Heaters are run for around an hour at a time, my thoughts are that the timer must have a tolerance for a couple of amps over it's official rating, so as all the cabling etc is well within spec might as well carry on using them. Does anyone know how long a 13a fuse should run with 16a going through it?

Cheers
 
I've got an old Bussmann BS1362 spec sheet here and it lists 1.6In as 30 minutes minimum and 1.9In as 30 minutes maximum.
 
Great, cheers - so for an hour at a time although not ideal it should be fine, as that's only 1.27xIn (plus they'll tick off and on it that time on thermostats so not on solidly). If they've fitted a 13a fuse to it they must have made sure the electronics inside can cope with extra current until the fuse pops, otherwise it wouldn't be much use would it!
 
Last edited:
Its not fine. The fused timer will only be rated to 13A so I'd suggest one heater is disconnected until the issue is rectified.
 

Reply to 2 x 2Kw heaters on 13a spur in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
132
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
914
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Electric hob/oven range was installed years ago, runs on 2 x B32 MCBs to 'House' (sub)consumer panel, runs to oven on 2 x T&E. Kitchen is being...
Replies
0
Views
345
The oven manual does say "fuse protection" now I checked it again. Energy consumption per cycle forced air convection (2010/30/EC)...
Replies
3
Views
187

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top