Two phases supplying two 2-pole RCDs in a consumer unit reconfigured as a small DB (with an external 3-pole main switch). Common Neutral.
In an outbuilding supplied by 10mm 4-core. TN-C-S ‘exported’ from main house by 10mm bonding. Local TT as an option in progress, awaiting tests before deciding.
L1 has 2 x 400W Metal Halide lamps through a 10A C-curve breaker, L2 ditto but 3 x MH’s. Plus other finals not finished yet.
One, or sometimes both, RCDs immediately trip when both phases are energized, and BOTH the MH lights switches (in the same grid switch box) are switched on. Only one circuit on, (L1 or L2) never any problem.
Disconnecting either phase supply from its RCD, then shorting the L1/L2 bus bars to run the whole panel (and all the lights) from only one phase and one RCD, the problem disappears. It’s fine whether L1 or L2 is used as the supply.
I’m stumped. I’m asking on here because it may be obvious to someone more experienced than me. Have I missed something fundamental?
Thanks, Mark.
In an outbuilding supplied by 10mm 4-core. TN-C-S ‘exported’ from main house by 10mm bonding. Local TT as an option in progress, awaiting tests before deciding.
L1 has 2 x 400W Metal Halide lamps through a 10A C-curve breaker, L2 ditto but 3 x MH’s. Plus other finals not finished yet.
One, or sometimes both, RCDs immediately trip when both phases are energized, and BOTH the MH lights switches (in the same grid switch box) are switched on. Only one circuit on, (L1 or L2) never any problem.
Disconnecting either phase supply from its RCD, then shorting the L1/L2 bus bars to run the whole panel (and all the lights) from only one phase and one RCD, the problem disappears. It’s fine whether L1 or L2 is used as the supply.
I’m stumped. I’m asking on here because it may be obvious to someone more experienced than me. Have I missed something fundamental?
Thanks, Mark.