Jimmyb

hi, will 2 x 250w metal halide lights be ok on a 6amp rcbo, i was hoping to use hager as the rest of the board was that and my suppliers only do type b will this be ok or will i need to source a 'c'

calc
(2x250)x1.8=900

900/230=3.91A
 
hi, will 2 x 250w metal halide lights be ok on a 6amp rcbo, i was hoping to use hager as the rest of the board was that and my suppliers only do type b will this be ok or will i need to source a 'c'

calc
(2x250)x1.8=900

900/230=3.91A
Ignore what your calculations tell you that is for cable calcs and switching size etc, you must obtain manufacturers recommendation when having multiple discharge lamps and depending what kind and size depends what they will recommend.
The answer to the above is a 10amp type (c) anything less is subject to nuisence tripping on start-up alternatively a 6amp type (d).
Hope this helps.

The best thing you can do is get hold of the product list book for each brand of breaker you use as these have the technical data in the back which has all this in it from motor to lighting - contactors to mcb ratings.
 
Last edited:

Reply to 2 x Metal halide in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

  • Question
Hi OnlQQker, Thanks for the information and the videos. I'll give them all a look, but the only problem I have is that my shop will be operating...
Replies
11
Views
2K
  • Question
My understanding is that, strictly, it's against the rules. Hopefully some on here can clarify. I know it doesn't stop people putting stuff in the...
Replies
5
Views
1K
  • Question
Usually a neutral to earth fault will trip the (RCD) part when current is drawn on the circuit, however i have also had a case where the same...
Replies
9
Views
4K
  • Question
Hi Andy, a big thanks for the reply, and yes a good point I hadn't considered there.. 6mm PVC should still do the job. T 1574171086 Hi West...
Replies
3
Views
2K
A
  • Question
Please try again as I've not received a message.
Replies
29
Views
12K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks