2 x Ovens and a hob - can anyone help? | on ElectriciansForums
Discuss 2 x Ovens and a hob - can anyone help? in the UK Electrical Forum area at ElectriciansForums.net
Tattyt
South West
Hi,
I have had an electrician out to look at at what needs to be done to install two new ovens and a new hob.
Existing: 6mm cable which was used for a double oven & hob previously, with one isolating switch. 40A breaker (think it should be 32A)
Two new ovens: Neff 2 x 2.99KW 13A
New hob: 6.5 KW
I just want to confirm that his recommendations are correct as it involves running some new cables so carpet, floor boards up etc etc.
If anyone could advise that would be brilliant :)
Hi,
New hob: 6.5 KW
Hi, welcome to the forums.
What has he recommended?
Hi SparkyChick,
Thanks for a prompt reply.
To run two new 2.5 cables, 2 x new 20 amp breakers with two new isolation switches.
Regards, Tattyt
crazy. unless the appliances are in separate areas. and depending on installation methods, 2.5mm may not be up to it.
They are approx 4 metres from the consumer unit but I have no idea the path of the cables.
The ovens are on top of each other and the hob is about 350 away from them.
350 what? miles, yards, poles, furlongs?
that's just over 1 foot. no reason not to feed all 2 ovens and the hob from existing 6.0mm (32A MCB/RCBO) via a 45A isolator and a dual connection unit. from the dual connection unit, feed hob in 4.0mm or 6.omm and each oven in 2.5mm (fixed loads do not require overcurrent protection for the 2.5mm).
If you were having a rewire or refit I would recommend a 2nd supply ....
But as others have said your existing set up could be adapted .....
Thanks Murdoch, no rewire or refit so new cable(s) would require a lot of work and stress!. If it does need to be done then so be it but it would appear not by the replies I have had.
I agree with above on face value. If it's in the onsite guide (as was) it's good enough for me...6mm cable 32a MCB up to 15kw...unless there's something else he is thinking of.
Edit..for cooker circuits obviously not showers
Reply to 2 x Ovens and a hob - can anyone help? in the UK Electrical Forum area at ElectriciansForums.net
Electric hob/oven range was installed years ago, runs on 2 x B32 MCBs to 'House' (sub)consumer panel, runs to oven on 2 x T&E. Kitchen is being...
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...