Hi All,
I have 1 X Fan oven 3.3Kw and an oven/microwave combo 3Kw. I had already installed a 4mm cable, as originally, there was only going to be one oven. After doing the calcs and looking at diversity, it seems to me that I'm safe to go with both ovens on this cable.
Total Load: 6.3Kw
Cable Rating: 37A
Reference Method: C (Cable is clipped direct to the ground floor joists above a concrete pad with plenty of air circulation. It is then clipped to a plywood wall as it enters the CU)
Load after diversity applied: 15.27A
Cable run to CU is 5M so voltage drop is negligible.
I welcome any constructive comments. Thank You.
Total Load: 6.3Kw
Cable Rating: 37A