A 20 amp DP switch is rated to switch a max load of 20 amps right?

Being told this afternoon that they can only be installed on a circuit that is fused at <=20 amps.:whatchutalkingabout
 
im in agreement with you amp. ive used them in the birds mums house instead of a fused spur, to isloate the washing machine, and dishwasher. a standard domestic socket is only rated to 13A per outlet, yet they are often installed on a 32A MCB.
 
disagree. the 20A switch's load is limited to what you connect to it. obviously, you would not connect a load exceeding 20A.
 
so expanding on that. an 80A Main Switch in a CU protected by a DNO 100A fuse is a no no then?
 
So connecting one to a circuit protected by a 30/32 amp fuse or breaker is not allowed even if used as a switch for a single socket ?
 
Surely as long as a load of less than 20A is drawn through that switch, it doesn't matter what the MCB is rated at?

If you were using it as an isolator for a single 13 amp socket for example, you'd be fine IMO.

I've got a 20A DP in my kitchen which isolates the 13A socket for the washing machine under the counter. Doesn't make any sense that this wouldn't be compliant.
 
Last edited:
So connecting one to a circuit protected by a 30/32 amp fuse or breaker is not allowed even if used as a switch for a single socket ?

The units are to BS1363, exactly the same as a twin or single 13A socket outlet.

The switching is rated at 20 Amps.
 
There was a bit of a debate about this very subject not long ago in another thread....
http://www.electriciansforums.net/electrical-forum-general-electrical-forum/38029-grid-wiring-kitchen-ring.html

M
y argument was that if you're feeding a socket outlet that's going to have something plugged in then the plug top will be fused.

Therefore, having a fused spur aswell would be pointless and would lead to discrimination issues as you'd have 2 fuses in series.

I see no point in fusing a 20A switch which is never going to be handling more than 13A.
 

Reply to 20 Amp DP switches in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
752

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
480
sounds like one of those jobs to swerve and let it be someone else's problem
Replies
12
Views
916

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top