Hi. All.

I have a trasnformer that takes 220v from wall and outputs 20 amp 5v to a string of leds.

I want to put a switch beetwen the wall and transformer. Could a regular lamp switch do it? or should a put a 20 amp switch?
 
Hi. All.

I have a trasnformer that takes 220v from wall and outputs 20 amp 5v to a string of leds.

I want to put a switch beetwen the wall and transformer. Could a regular lamp switch do it? or should a put a 20 amp switch?

The 20 amps is what the load will take from the secondary of the transformer. The input current will be much much less.

Remember, the transformer power in will be roughly the same as the power out, ignoring the various losses. So you can use Ohms law and get a rough idea of the input power, and therefore what the rating of the switch needs to be.
 
Hi. All.

I have a trasnformer that takes 220v from wall and outputs 20 amp 5v to a string of leds.

I want to put a switch beetwen the wall and transformer. Could a regular lamp switch do it? or should a put a 20 amp switch?
A switch conglomerate with the load it is going to switch
 
The input power will be 120-150VA i.e. less than an amp at 220V. But you should allow for inrush (surge at switch-on) and fit a switch with higher rating than 1A. In the absence of more detailed information, I would usually choose a part rated at 5A or 10A for this application to ensure it is tough enough to withstand the inrush.
 

Reply to 20 amp transformer switch question in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
417
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Better off with the click prw213 as it has twin screw termination.
Replies
9
Views
995
It's unlikely tht a small domestic garden pump and a single lamp will come anywhere near close to overloading even the smallest (3A) fused spur...
Replies
2
Views
442

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top