E
emlyn
Hi. Have back fed this transformer trying to achieve 400 volts from a 250 volt 50Hz 3 phase 20Kva diesel powered generator. Have linked the high voltage Delta connected side to include all the windings, and connected the generator to the star connected low voltage windings, leaving the neutral unconnected. Transformer checks out ok, but I can only achieve about 260 volts per phase at the high voltage terminals, with no load. When a 400 volt 2 HP motor was connected as a load, it obviously wouldn,t operate properly, but the current from the generator was measured at 20 amps per phase, and making the engine work quite hard! Would appreciate any suggestions. Thanks