Thought that when doing a MWC you were to test the circuit you have modified, not just your new bit.

Section 3 on the MWC is titled, INSPECTION AND TESTING OF THE MODIFIED CIRCUIT AND RELATED PARTS. to me this means all of it[FONT=Calibri, Arial, Helvetica, sans-serif]https://www.parcel2go.com/dhl-parce...ml_dhltrackingalert&type=email&location=email[/FONT]

It doesn't state such on the model forms in BS7671.
There are 4/5 essential tests listed that should be caried out, some of them will include the existing part of the circuit.
Such as earth continuity, IR and perhaps if applicable an RCD test.
Now if you want to check Zs, polarity correct etc. at each point on the circuit, please do so, just be aware that it is not a requirement of BS7671 to do so.
 
Yes you must be.
I asked you where you would test Zs, and you have stated at the highest R1+R2 point.
What about at the point where you have conducted the work? How would you determine where the highest R1+R2 point is?
The MWC asks for earth continuity, IR, Zs and polarity, but you have stated that you would not do Zs?
Make your mind up, either you would conduct a Zs test at each point or you wouldn't.
Recently I was asked to install a light in someones porch.
Simple matter as the CU was on the other side of the wall from where the light was to be positioned.
Run a feed from the downstairs lighting MCB to the fitting and then a switched line from there to the 2 gang light switch in the hall which was replaced with a 3 gang switch.
Should I then go to their downstairs bath room at the rear of the house, and drop out all the down lighters out of the newly decorated ceiling to establish which has the highest R1+R2 and then test the Zs?
How would that establish that the wiring I had installed had earth continuity, correct polarity and acceptable Zs?
 
Never once stated I wouldn't do a Zs test.

With your litle porch light you'd of tested R1 R2, and proved polarity. Your Zs would be taken fronm furthest point on the circuit, might be the porch might not.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
20a DP switch for light
Prefix
N/A
Forum
Electrical Tools and Products
Start date
Last reply date
Replies
21

Advert

Thread statistics

Created
still learning.,
Last reply from
Amp David,
Replies
21
Views
12,006

Advert

TrueNAS JBOD Storage Server

Back
Top