Hi everyone, I'm currently upgrading my workshop and before I get quotes for the electrics I'd like to understand it better myself. If I want 6 sockets from a ring mains circuit can I spur off an existing socket to a 20a DP switch and run the 6 sockets from that? It's unlikely the load will exceed 4kw, there will be an electric heater running, as well as a kettle, microwave and occasional use of electric saw etc. Or would I be better off running 3 sockets each from two separate 13a FCU switches spurred off two different sockets on the ring circuit . Any advice would be appreciated many thanks.
 
no you can't spur off a ring without fusing down. for the load you anticipate, you need to extend the ring. i.e. split at convenient socket and loop round the workshop, making all of the sockets on the ring. should end up with something like this. 2 existing cables and 2 new cables .
 

Attachments

  • [ElectriciansForums.net] 20a DP switch spur for 6 sockets
    rfcextend.jpg
    237.8 KB · Views: 39
Last edited:
no you can't spur off a ring without fusing down. for the load you anticipate, you need to extend the ring. i.e. split at convenient socket and loop round the workshop, making all of the sockets on the ring. should end up with something like this. 2 existing cables and 2 new cables .
I see many thanks for the reply telectrix.
 
As above, best option is to extend the existing ring final, after checking that:
  • It has RCD protection, and
  • The ring is OK (end-end continuity and insulation resistance good)
(OK, just read that you have an RCD, but leaving it for anyone else reading this in the future)
 
One final though, presumably you don't actually need an isolation switch (or emergency stop) for any other workshop safety reason?

If it is just for hobby stuff without any seriously intimidating equipment then just go with the ring extension. Otherwise if you really need some means to isolate the whole area you would be better with a separate 4mm radial from the CU just to feed the 6 sockets via a local isolation switch.
 
One final though, presumably you don't actually need an isolation switch (or emergency stop) for any other workshop safety reason?

If it is just for hobby stuff without any seriously intimidating equipment then just go with the ring extension. Otherwise if you really need some means to isolate the whole area you would be better with a separate 4mm radial from the CU just to feed the 6 sockets.
My understanding was that you could only spur off to multiple sockets if you had a fused switch coming off the ring first. And because I planned to be able to run an electric heater, kettle and microwave at the same time for example I presumed that would blow a 13a fuse, hence why I presumed a 20a DP switch could just be used instead. I'll be getting a professional round at some point but would be handy to know the options beforehand. Also the CU is a fair distance from my workshop hence why I thought the spur would be easiest/cheapest option!
 
a 20A D/P switch is no good. it's not fused. you could fit a 20A MCB in a small enclosure to feed a spur, but for the load you mention,better as a ring extension (you only need to access a local existing socket, no need to go back to CU) so you have a 32A capacity. the 32A MCB will allow small overloads for short time periods without problems.
 
a 20A D/P switch is no good. it's not fused. you could fit a 20A MCB in a small enclosure to feed a spur, but for the load you mention,better as a ring extension so you have a 32A capacity. the 32A MCB will allow small overloads for short time periods without problems.
Excellent, many thanks for your feedback telectrix much appreciated.
 
My understanding was that you could only spur off to multiple sockets if you had a fused switch coming off the ring first. And because I planned to be able to run an electric heater, kettle and microwave at the same time for example I presumed that would blow a 13a fuse, hence why I presumed a 20a DP switch could just be used instead. I'll be getting a professional round at some point but would be handy to know the options beforehand. Also the CU is a fair distance from my workshop hence why I thought the spur would be easiest/cheapest option!
Extending the ring maybe your cheapest and easiest option but if you intend to use the workshop on a regular basis with multiple equipment, then personally, if its an option, I would seriously consider a separate supply from the CU.
 
I would look at running a separate circuit for your workshop. Last thing you want is something tripping the power and taking out a circuit in the house as well.
 
I would look at running a separate circuit for your workshop. Last thing you want is something tripping the power and taking out a circuit in the house as well.
Many thanks for the reply, out of interest if I extended the ring circuit would that mean the max possible amp on the circuit would be 32A before it trips?
 

Reply to 20a DP switch spur for 6 sockets in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
951
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

J
The rcd spur being fitted is probably because there wasn't rcd protection of that supply.
Replies
5
Views
441
K
  • Question
Ah, I see. The op question is ambiguous, and I took it that he wanted to add a socket for a washing machine from and exiting switch fused spur. A...
Replies
10
Views
906

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top