W
willf
Hi folks
Got my 2330-302 practical tomorrow and pretty confident but just wanted to double a couple of things if anyone can help. On the test rig there is the usual lighting & RFC's but also a shower, motor (switched thought a dol starter) and a bathroom fan. Just wanted to check the procedure for R1+R2 and IR tests.
Shower - Disconnect at shower for R1+R2 and IR and remove neon in pull-switch (or bridge out)
Motor - I guess for the R1+R2 I will have to do two tests for R1+R2 and add them together. Test to the DOL starter and then from the DOL to the motor? Not sure about the IR test though.
Bathroom fan - Disconnect from fan for R1+R2 and IR?
Also got to do Zs but as we can't work live (HSAW) I guess I can calculate these from Ze+R1+R2 and just do direct measurements for sockets?
Got my 2330-302 practical tomorrow and pretty confident but just wanted to double a couple of things if anyone can help. On the test rig there is the usual lighting & RFC's but also a shower, motor (switched thought a dol starter) and a bathroom fan. Just wanted to check the procedure for R1+R2 and IR tests.