kmatthews

quetion: the earth fault loop impedance measurement on a socket protected by a type c circuit breaker is over the limit permitted by bs 7671 tables. there is no fault with the wiring, suggest two methods which may be used to overcome this problem?
 
The other option would be to break the circuit into two.
And split it over 2 mcb's.
This will also lower the resistance of the cpc due to the shorter length of the circuit.
Obviously these aren't necessarily practical solutions, but purely theory.

However it demonstrates knowledge of the effects of increasing csa or decreasing the length of the cpc.
 
Upvote 0
yea that would work but im my question is suggests that there is nothing wrong with the wiring.

thats what got me a little confused.

if its not a problem on the wiring it can rally only be the protective device or the load applied?
 
Upvote 0
Agree with swopping to type b mcb as it has a higher Zs tolerance.

But how is fitting an rcd part of the answer to this question ?
How does fitting an rcd lower the Zs ?

The other answer could also be to increase the csa of the main bonding conductor. This will lower the Ze value and therefore the Zs for this circuit.
 
Upvote 0
That's the answer C&G are looking for the question does ask how to overcome the high zs problem not how to lower it, we had this in a practice paper last week.


Sent from my iPhone using Tapatalk
 
Upvote 0

Reply to 2330 exam in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
740

Similar threads

  • Question
He is after the four options for 1 and 2 of the multiple choice exam, probably optimistic someone will know this. Your question 3 in incomplete to...
Replies
2
Views
1K
  • Question
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top