Based on your current circuits I notice that every Zs calculation shows the circuit length as 30m, but then the results do not match wit
For the lighting circuits not knowing the circuit length makes it impossible to calculate Volt drop, however, you have three lighting circuits with different design currents and presumably different lengths and yet the calculated volt drop is the same in each case. The values also seem high unless you have very long circuits perhaps you could show your working there.
The pump room equipment appears to be a single circuit and presumably not grouped as it is clipped direct SWA yet you have a grouping factor of 0.73, I cannot work out where this is derived or why but you may have more information about it.
Check your maximum permitted volt drop for this circuit as well.
For installation method it is common convention just to use the letter e.g. C rather than including the installation method number e.g.20, however including the number does give more information so could well be useful.
The scale of 1:50 means for every 1 it is 50 full scale. So 1cm on your plan equates to 50cm in reality.
Are we taking this course or are you?How we are to do the length of the circuit, is by measuring each circuit, we have a scale drawing 1:50, on A4, however that has been submitted for critique marking, As that was Q2 were we needed to draw the lighting circuits for each room, as I am only allowed to take certain questions home. I thought it best to use the maximum allowed which was 30M As we have to fill in a table at the very end in pencil, I can just change some of the calculations once Q2 which is the drawings has been marked and given back to me for any changes.
Are we taking this course or are you?
See my responses in red aboveSo I had a go, based on those calculations:
2.5mm² CPC is suitable.
- Ib 16A YES
- In 16A YES
- Method of Installation: C Not known I thought cafe power was PVC singles in conduit (B) but fridges may be different.
- Rating Factor: 16/0.94x0.80 = 21.27A YES 35°C two grouped circuits
- It 2.5mm2 24A VD 18 Suitable YES
- Actual VD: 18X12X16/1000 = 3.456V For a 12m circuit YES
- Max VD: 11.5V Correct, non lighting circuit
- Max R1+R2 2.73-0.11/1.2x12 = 181.94Ω NO Maximum permissible R1+R2 for circuit at 20°C = Zs-Ze/1.2 =2.18Ω, useful to do a "sanity check" on your answers, you are working in the mΩ and low single figure Ω range for circuit resistances is 182Ω a likely result?
- Calculated R1+R2 7.41+7.41x1.2x12/1000 = 0.11Ω YES at normal operating temperature
- Calculated Zs 2.73x0.8 = 2.18+0.11 = 2.2Ω I would say 2.3Ω (round up) However Zs = Ze +R1+R2, you have used tabulated maximum Zs corrected to 20°C not the given Ze which I think was 0.11Ω, confusingly the same as your R1+R2.
- Fault Current: 230/2.2 = 104A Maths correct but these results are affected by the above paragraph
- S = Square Root: 104² x 0.1/115 = 0.28mm² Maths correct but these results are affected by the above paragraph
From my point of view you have specified Type B for the MCBs for all circuits except the Fridges, therefore you need to specify what type MCB you will use for the Fridges.
The Fridges are quite large, it appears; as I said in an earlier post most commercial fridges would not exceed 500W (2.1A). However a fridge, since it is running a compressor motor, when started does have a high peak current. This current might be 10X the normal running current but for a fraction of a second. If you only had one fridge on each 16A radial circuit then the peak current of, say 21A, would not trip the 16A type B circuit breaker. If you had six fridges on one 16A circuit and they were all started simultaneously then it is possible the peak current could trip a 16A type B breaker and you may wish to select a type C breaker to ensure this high starting current did not trip the breaker.
Functional earthing is generally only found in things like PELV systems or RCDs with functional earthing conductors. Functional earths are an earth reference that is not intended to provide a safety function. If the conductor is both functional and protective then the CSA is determined by the protective part, if just functional then by the minimum CSA given in table 52.3 in section 524.
Main protective bonding is covered in section 544.