Hi,

I was hoping for some advice regarding testing a circuit with a dol start in it? As ive not yet work on one.

[ElectriciansForums.net] 2391-52 dol starter question


I was thinking for R1+R2 i could test L1 at the db to L1 on the dol input & then L1 output on dol to plugs then add them & r2 to get R1 + Would this be ok for the exam practical?

Was thinking for IR i could test L1 to L2/3 at the db & then L1 to L2/3 on the output side of the dol? Basically testing each side of the dol separately

Zs could be taken a plugs socket or could be calculated via Zs=Ze + (R1 + R2) method.

Hope that makes sense

Got my practical tomorrow & all my revision is making my brain turn to mush now + i dont like exams lol

Any advice greatly received

Thanks

Michael
 
Hi,

I was hoping for some advice regarding testing a circuit with a dol start in it? As ive not yet work on one.

View attachment 38242

I was thinking for R1+R2 i could test L1 at the db to L1 on the dol input & then L1 output on dol to plugs then add them & r2 to get R1 + Would this be ok for the exam practical?

Was thinking for IR i could test L1 to L2/3 at the db & then L1 to L2/3 on the output side of the dol? Basically testing each side of the dol separately

Zs could be taken a plugs socket or could be calculated via Zs=Ze + (R1 + R2) method.

Hope that makes sense

Got my practical tomorrow & all my revision is making my brain turn to mush now + i dont like exams lol

Any advice greatly received

Thanks

Michael
Personally I would carry out safe isolation of the Motor circuit, link the three phases at the contacter and carry out your tests.
 
When I did that (DOL starter test), I just did a continuity test and established there was no connection on L1 or to put it another way the L1 had a break, that was it.. I was asked to establish what the fault was and that was it. Oh and I was asked to look at the rating and statewhether it was adequate for the motor. The writing was really really small Oh and best of luck with the exam by the way!
 
[ElectriciansForums.net] 2391-52 dol starter question

How do i know if dol has thermal cut out?
Is that the blue bit by the dials?

Thanks for all the advice

Ok so for R1 +R2 im going to connect L1 & r2 together at the db, link across the L1 input & out put on the dol & plug the megger into the plug socket. Then repeat this for L2 L3 - recording the highest reading.

Regarding IR testing:
if testing at the db while the L1,L2 & L3 are connected to the input connector on the dol would this be ok or would it damage it? Also would it be ok testing on the dol out put side while L1, L2 & L3 are connected.
Worried about the thermal cut out being an issuse when IR.


Thanks again
 
Ok so after searching google it looks like the whole bottom bit that has the dials & blue bit incorporates the thermal cut out.
Left dial is amps setting next dial is manual or automatic reset & the blue bit is the manual reset button
 
You're correct.

In regards to testing, IR and continuity will not damage that basic thermal overload module and should have no ill effect to results. Unless there is something wrong with it. (Be careful in future if you come across electronic ones).

Last AM2 examination place my apprentices went had them link out both the contactor and the overload. Although just bypassing the contactor is all that's needed.

Make sure the dial is set to the correct current rating.
 
Thanks rob for clarifying that for me.
As always everyones really helpful here
 
View attachment 38243
How do i know if dol has thermal cut out?
Is that the blue bit by the dials?

Thanks for all the advice

Ok so for R1 +R2 im going to connect L1 & r2 together at the db, link across the L1 input & out put on the dol & plug the megger into the plug socket. Then repeat this for L2 L3 - recording the highest reading.

Regarding IR testing:
if testing at the db while the L1,L2 & L3 are connected to the input connector on the dol would this be ok or would it damage it? Also would it be ok testing on the dol out put side while L1, L2 & L3 are connected.
Worried about the thermal cut out being an issuse when IR.


Thanks again
Just finished my 2391-52 practical tests, photo fault coding & written questions.
Well chuffed as i PASSED
Good Man
 

Reply to 2391-52 dol starter question in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
298
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
848

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top