T
ta-electrical
Hi, got a question from the 2391 exam that i need answers for, any help would be appreciated.
You'll need the following information to help answer the question;
- It's a TT system
- Electrode resistance (Ze) = 29 ohms
- BSEN 60898 maximum Zs = 8.0 ohms
- Length = 60m to furthest point of circuit
___________________________
Conductor CSA | mΩ/m at 20°C |
__1.0mm ____|___ 18.1______ |
__1.5mm ____|___ 12.1______ |
a) Calculate R1 + R2 for circuit if CPC is 1mm2 copper conductor (show all calculations)
b) Determine the value of Zs and say why it meets BS7671 requirements for the BSEN 60898 device (show all calculations)
c) State with reason what action would be taken if circuit fails to meet requirements
Thanks in advance.
You'll need the following information to help answer the question;
- It's a TT system
- Electrode resistance (Ze) = 29 ohms
- BSEN 60898 maximum Zs = 8.0 ohms
- Length = 60m to furthest point of circuit
___________________________
Conductor CSA | mΩ/m at 20°C |
__1.0mm ____|___ 18.1______ |
__1.5mm ____|___ 12.1______ |
a) Calculate R1 + R2 for circuit if CPC is 1mm2 copper conductor (show all calculations)
b) Determine the value of Zs and say why it meets BS7671 requirements for the BSEN 60898 device (show all calculations)
c) State with reason what action would be taken if circuit fails to meet requirements
Thanks in advance.