A three phase 400/230V electrical installation within a ten year old commercial unit for sales and storage of medical equipment forms part of a TN-C-S system and is to be inspected and tested. Ze was measured as 0.09 Ohms.
Following a small fire in the office area three lighting circuits and three ring final circuit require re-wiring. On completion of the work the client requires all relevant documentation for the installation for insurance purposes.
The existing metal clad TP & N distribution board contains BS EN 60898 type B and C
circuit breakers.
The existing surface mounted wiring system consists of 70C thermoplastic insulated
single core cables in metal conduit and trunking in the warehouse area.
Plastic conduit and trunking is used in all the other areas.
The new lighting circuits are wired in 1.5mm single cores 70C thermoplastic insulated cables.
The new circuits are 18, 24 and 32 metres in length respectively.
The resistance per metre for a 1.5mm single conductor is 12.10 mOhms/M.
State giving reasons the documentation to be competed for the work stated above.
I was thinking six minor works certificates for the three lighting and ring circuits because they are not new circuits they are re-wired old circuits and they would most likely follow the same route as the old cabling and be wired in the same size cable.
The method of fault protection would be the same.
Then a PIR for the rest of the installation.
What do you think?
Gracias.
Following a small fire in the office area three lighting circuits and three ring final circuit require re-wiring. On completion of the work the client requires all relevant documentation for the installation for insurance purposes.
The existing metal clad TP & N distribution board contains BS EN 60898 type B and C
circuit breakers.
The existing surface mounted wiring system consists of 70C thermoplastic insulated
single core cables in metal conduit and trunking in the warehouse area.
Plastic conduit and trunking is used in all the other areas.
The new lighting circuits are wired in 1.5mm single cores 70C thermoplastic insulated cables.
The new circuits are 18, 24 and 32 metres in length respectively.
The resistance per metre for a 1.5mm single conductor is 12.10 mOhms/M.
State giving reasons the documentation to be competed for the work stated above.
I was thinking six minor works certificates for the three lighting and ring circuits because they are not new circuits they are re-wired old circuits and they would most likely follow the same route as the old cabling and be wired in the same size cable.
The method of fault protection would be the same.
Then a PIR for the rest of the installation.
What do you think?
Gracias.