Greetings all.

I am trying to get a few things straight in my head before Tuesday.
The main thing I am not sure about is this three phase motor starter.
The way I was gong to tackle it was to R1+R2 it.

Starting at the DB link L1 -E, get examiner to hold contactor and measure at the socket and record.
Then link L2-E and do the same, then link L3-E and do the same, record the highest value.
Add value to the measured Ze and compare results to tables in BS7671 to see if EFLI values are
low enough to comply.
Any comments welcome

The thing I am not sure about is IR testing the board as a whole in one hit with the DOL starter attached.
Is the DOL starter vulnerable to IR testing at 500V?
I have read quite a few posts and can't seem to get a straight answer.
I understand that the starter must be tested in two halves, one half from the board to the starter
and the other half from the three phase socket end to the starter but do we need to actually take the wires out of the DOL starter before IR testing?
Can we put 500V across the terminals of the DOL starter without damaging it?

This DOL starter is the only thing I am really not sure about and any advice would be appreciated.
Thanks.
 
The examiner will not hold the contactor in mate. I was told (and did it this way and passed) to measure from DB to contactor then from contactor to socket, add the two measurements together and thats the (R1+R2)
Similarly with the IR for that part of the test rig test to the contactor then away from it.
 
The examiner will not hold the contactor in mate. I was told (and did it this way and passed) to measure from DB to contactor then from contactor to socket, add the two measurements together and thats the (R1+R2)
Similarly with the IR for that part of the test rig test to the contactor then away from it.


Agreed. Your examiner wont be holding anything in for you.

Break it down into 2 steps.
 
Just had an idea how to speed up the DOL test.

Why not do an R2 test on the CPC, and also an R2 test on L1, L2, L3 then add together line and CPC to give you R1+R2.
You could connect one end of the long lead to the socket and the other to the board and then press the DOL in manually.
That would save a load of time joining line and CPC at the board and measuring one half of the circuit up to the DOL and then having to join line and CPC at the socket and having to measure the second half of the circuit from the socket to the DOL.

I just wonder what the assessor will think of this method.
 
I asked the assessor before the test and he said the preferred method was to R1+R2 in two halves and then add them both together but he also said only do one line, don't bother about the other two which I think is wrong.

Anyway I passed just about.

What I also think is wrong is the two hour time limit.
If you really want to do it properly and check disconnection times for each circuit, terminations and everything then two hours is not enough.

I don't know what to think but I passed that's the main thing and now I'm away on the ----.

Cheers all.
 
Well done on the pass!
The time limit is there just make sure you know what you are doign and not muddling through blindly, you get faster with practice. And the main thing outside is get it done now! Unfortunately.
 
Yeah it was a funny old test.

12 faults, insulation resistance fault, EFLI fault and a PIR.

I hope the 2391 is worth something after it suddenly changes number to a new exam.

It's a good exam.

It really tests you, it really tested me to the limit.
 
Last edited:
Yeah it was a funny old test.

12 faults, insulation resistance fault, EFLI fault and a PIR.

I hope the 2391 is worth something after it suddenly changes number to a new exam.

It's a good exam.

It really tests you, it really tested me to the limit.


hopefully it'll be worth even more :)
 
Not a chance!!!
History says that the "new" qual will be the bees knees, even if its pants.

I wonder if employers get fed up with it.
The numbers keep changing I mean.

I was lucky on the 2391 the examiner was helpful, he made a lot of allowances for exam nerves.
And the DOL had three little home made sockets for your testing probes to fit in just nicely.
Making it much easier than trying to crocodile clip on a socket.

He said at the beginning the board has no faults but I found three.
The biggest one was he said it was TN-S and when I IR'd neutral to earth I got zero ohms.
I was taking neutrals out of the board and re-testing and wasted 20 minutes with him trying to figure it out and then he said
Ahhh and pulled the main plug to the board out of the mains, even though it was switched off with a rotary switch
the supply to the switch is TNC-S and hence no reading between neutral and earth.
So there were a few cock ups on his side.
The biggest issue was time though.
It's a hell of a race to get it all done in two hours.
 

Reply to 2391 practical DOL starter in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
298
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
848

Similar threads

  • Question
I believe that it is incorporated into the 5 days. But will double check. Thanks.
Replies
6
Views
990
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top