Thanks guys,
Just a few more questions if you dont mind,
I have been told that as part of the exam there is small rig with 12 faults on it,am i right in assuming that this is just a visual inspection & i'm basically looking for things like loose connections,to much copper showing,reverse polarity etc?
Yes a lot of little things on a small board - i remember the last fault i found was a 13A fuse in an fcu to lighting.
Also when doing IR tests i tend to do 1 circuit at a time but due to time constraints was going to do the IR test on the main rig for the PIR as a one main one for the whole board so was wondering what is the best & quickest way to do this bearing in mind that it will incorparate a least 1 RCD?
As i said earlier, we had an rcbo - removed that and put in pocket - made a little table for results and tested all lines to N, all lines to cpc , and L1 to L2 etc .Then did the circuit that had the rcbo on.
Finally as far as the exam is concerned theres the PIR on the main rig,the 12 visual faults,& apparently faults to be found doing an IR test
Yep very straight forward - 3 circuits if i recall and just had to find and identify what the fault was eg open circuit between L and N
& one more unit that i dont know could anyone please enlighten me?
We also had a Zs test to do and check if value was acceptable - just had to remember to look in the correct table in BS 7671 and use 0.8 (rule of thumb) of value in the book
.Many thanks