Your practical will consist of 4 assessments.
Assessment 1:
Visual Inspection Exercise - 30 mins
You will be shown a test rig and given some paperwork. You will be expected to find 'x' amount of faults that are visually identifiable. These faults are dictated by City and Guilds, and are not the genius craft of the training center themselves.
No test equipment will be necessary for this assessment. The assessor will have a crib sheet with the exact faults (12 in total) and you need to identify all of them.
Assessment 2:
Insulation Resistance Exercise - 20 mins
You will be shown to another test rig where you will be introduced to the insulation test assessment. You will be expected to be able to select the necessary test, check it for calibration, check it for damage and choose the correct settings accordingly.
You will be given a sheet with the information to record 2 tests. You will carry out the first test within your first 10 minutes and the assessor will switch in another scenario for your second test, taking the final 10 minutes.
You will do bunch testing for the insulation resistance. A particular scenario will be introduced on the first test by the assessor and it will co-ordinate with the crib sheet so that they know what readings they are to expect.
For each test you will identify the location of the fault (circuit number and description), the polarity of the fault (between Live conductors or between Neutral and Earth etc) and the nature of the fault (short circuit or low resistance).
Assessment 3:
Earth Fault Loop Impedance - 10 mins
This quickie little assessment will involve you again correctly selecting and checking the necessary tester. The assessor will show you to a socket outlet where a pre-recorded or controlled value of Zs is located. You will measure the Zs, take note on your record sheet of the type of protective device and it's rating. You will then follow appendix 14 of BS7671 or use the relevant table in the OSG and calculate the adjustment to the tabulated value for correction due to the operating temperature.
You may also be given an ambient temperature, which if it is anything other than 10 degrees, will result in the application of a correction factor that you will select from the relevant areas in the OSG.
You will do this test twice in the 10 minutes.
Assessment 4:
Periodic Inspection Report - 120 mins
The big one.
You will be shown a rig consisting of a TP&N consumer unit, with another SP board fed from it. Final circuits from the TP&N will be a ring final, a fuse spur (supposed to be in MI, but oftenly now installed in FP200) and a motor control in SWA. The SP board will have a radial socket outlet, and RCD within the board, and lighting circuits consisting of two way lighting and a dimmer switch.
You will be expected to carry out a full periodic inspection and test with all the reporting carried out.
All equipment must be correctly selected, checked and used.
Great consideration needs to be given to the safe isolation procedure with regard to locking off, warning signs, proving isolation with a proving unit and a GS38 compliant tester. Make sure you put the key in your pocket when locking off.
It is part of the assessors duty to display an arrangement of test equipment beyond the requirements of your assessment, this creates the challenge for the delegate to correct select the equipment. It is also a requirement with some assessments to deliberately place a voltage indicator that does not conform to GS38, proving as to whether the delegates correctly inspects the test equipment or not on selection.
This assessment alone will require a handful of test:
Continuity of protective conductors (cpc's and bonding)
Continuity of ring final circuits
Insulation resistance (be particularly aware of the dimmer switch)
Polarity (dead, then live)
External earth fault loop impedance
Prospective fault current (PEFC, PSCC, highest value become PFC)
Earth fault loop impedance
RCD