CRAGS

For the 2391 Practical when you test the SP+N consumer unit for ZS and ZE which I am guessing is one test is it just L-E ???? Or do you do L-N as well I did make some notes last night but L-N does not seem right ???? Thanks in advance
 
If your testing at the single phase board, which is a sub-main off the 3 phase board, then you are testing both Zs, and the PFC of that sub-main circuit.

Ze will only be measured at the incomming supply to the 3 phase board.
 
Upvote 0
We were told to measure Zs for the single phase board (Record on three phase test sheet as Zs for SP +N) and record the same figure on the SP test sheet for the Ze.

But how do you do the test ???? I thought Zs for lighting or socket was live earth neutral but I am sure we only did live and earth last night
 
Upvote 0
Ok so on the main certificate for the 3 phase board, the sub-main to the single phase board will be one of the circuits so you record R1+R2, I/R, Zs etc.

On the continuation sheets that accompany the main certificate the single phase board becomes the main board if you like, with all of it's circuits then listed in the continuation schedules.

Usually (on NIC forms at least) at the top there are two boxes that are filled in when the CU is not connected directly to the origin, i.e a sub-board fed via a sub-main. In these boxes it asks for "chracteristics at this distribution board" this is where you measure the Zs or Zdb as it's also known and the PFC.

I find it funny that they would tell you that this should be recorded as a Ze value as it isn't.

Earth fault loop impedance can be measured using a two or three lead instrument, as can PFC.


Hope this helps.
 
Upvote 0
He did mention about recording it as zbd. I think it is the way the boards are set up that he is telling us to record it that way???

I know how to do the pfc test I.e. L-N L-E

But what about the ZS can that be done on 2 lead by just L-E ???

Thanks again
 
Upvote 0
Yes got a copy of guidance notes 3 it just threw me that on the ceiling roses for Zs we were doing E-L-N and on the SP unit we were only doing L-E The meter is a megger 1502
 
Upvote 0

Reply to 2391 Practical ZS in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I believe that it is incorporated into the 5 days. But will double check. Thanks.
Replies
6
Views
1K
  • Question
Yes, for example: https://kingsmillindustries.com/product/km2-20-10-sc/ However, the reality is the L-N-E style are far more useful in general as...
Replies
2
Views
999

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top