Hi all, I got given a past exam paper from the 2391 course tutor however it doesnt come with any answers so I thought id put the question and my answers on here to see if im going down the right track and also to help anyone else taking this course so please correct me if im wrong because I probably am.
Q1. BS 7971 requires an inspection to be made on installed electrical equipment during the initial verification. State the three areas to be verified.
A1. .All electrical equipment and materials are of the correect type and comply with all relavent British Standards
.All part of the fixed installation are correctly selected and erected
.No parts of the fixed installation is visually damaged or otherwise defective
Q2. a) Two items of information regarding the protective device at the origin, to be obtained from the distribution network operator.
b) What the designer may take into account when determining maximum demand
A2. a) The rating of the device and its rated short circuit capacity
b) The full load of the installation with diversity applied
Q3. State one statutory and two non statutory publications which relate directly to the inspection and testing process
A3. Statutory - Electricity at work regulation, Non Statutory - BS7671 and Guidance note 3
Q4. A steel conduit and trunking installation has been erected and is to be inspected prior to the installation of cables. State three inspection items which will be checked using the sense of touch.
A4. No sharp edges, conduit is reamed and bushed
Trunking lids are secure
All conduit trucking and accessories are securely fixed
Q5. The electrical installation in a sandwich bar is to be inspected and tested in order for the owner to obtain a license from the local authority. State
a) the two parties with whom the inspector must discuss the requirements for the inspection and test
b) where the outcome of the discussion is to be recorded
A5. a) The local authority and the sandwich bar owner
b) On the periodic inspection report form under extent of installation inspected and limitations.
Q6. List three operational characteristics of a low resistance ohmmeter as identified in guidance not 3.
A6. .No load voltage between 4V and 24V
.Short circuit current not less than 200mA
.Test current a.c and d.c
Q7. a)State two reasons for the prescribed sequence of test prior to energising a new circuit.
b)State one test on an installation forming part of a TT system which may be carried out as either a live test or a dead test.
A7. a)To ensure that the polarity is correct and that no short circuits exist on the installation prior to energising it.
b) Resistance of the earth electrode (Ze)
Q8. State one method of verifying each of the following (each method must be different)
a)Continuity of a lighting circuit CPC
b)Continuity of a main protective bonding conductor 40m in length
c)Continuity of the earthing conductor
A8. a)R1 +R2 test
b)Wandering lead test
c) Ze test
Q9. A conductor of length 50m has a resistance of 2.3mohms/m. A second identical conductor is to be installed in parallel with this conductor. Determine the total resistance of these two conductors when connected in parallel. Show all calcs.
A9. Resistance of conductor = (2.3 x 50)/1000 = 0.115
1/RT = 1/R1 + 1/R2
1/RT = 1/0.115 +1/0.115
1/RT = 17.4
RT = 1/17.4
RT = 0.057 or 57mohms
Q10. State a)two factors which will reduce the insulation resistance of a new installation measured at the distribution board with all the circuits connected.
b)the voltage to be applied when testing the insulation resistance of a 400V ac circuit
A10. a) Number of circuit connected in parallel
b) Length of circuit (decrease when longer)
Q11. A circuit which includes surge protection devices is to be tested to determine insulation resistance. State
a)two methods recognised in BS7671 for safely testing this circuit
b)the minimum test voltage which can be applied
A11. a) Remove surge protection and link out or if not possible test with reduced test voltage
b)250V dc
Q12. An insulation resistance test is carried out on each of the following circuits. State the test voltage to be used in each case.
a)25V SELV lighting circuit
b)650V three-phase motor circuit
c) 110V reduced low voltage circuit
A12. a)250V DC
B)1000V DC
C)500V DC
Q13. State three special locations identified in BS7671 which are divided into zones
A13. Swimming pool, Area containing a bath or a shower, A sauna
Q14. State the appropriate IP protection to be provided for the
a)top surface of a readily accessible motor starter
b)front of a readily accessible distribution board
c)internal barrier within a consumer unit where the cover can be removed without the use of a tool or key
A14. a)IPXXD
b)IPXXB
c)IPXXB
Q15. A BS 1361 fuse is to be used to provide overcurrent and fault protection for a new circuit. State the effect on the operation of the fuse when the following conditions occur if the fuse was installed in the neutral conductor,
a)overload fault
b)earth fault
c)short circuit fault
A15. a)Fuse will operate however the supply will not be cut off
b) The fuse will not operate
c) The fuse will operate but the supply will not cut off
Q16. State a)The test instrument used to measure the earth electrode resistance for
i/ a generator
ii/ an installation protected by an RCD and forming part of a IT system
b)the number of readings to be taken for the test in a)i/ above.
A16. a) i/Earth electrode resistance tester
ii/Earth loop impedance tester
b) 3
Q17. State a)two methods by which the external earth fault loop impedance (Ze) may be determined
b)one method of determining Zs when direct measurement is not possible (Not Ze)
A17. a)Driect measurement and enquiry
b)Calculation Zs=Ze+(R1+R2)
Q18. State the maximum permitted time/current performance criteria for a 30mA BS EN 61009 RCBO when tested at
a)15mA
b)30mA
c)150mA
A18. a) No trip
b) 300 ms
c) 40 ms
Q19. a) List the two test measurements to be taken in order to determine PFC at the origin of a single phase electrical installation
b) State which of the measured values is to be recorded
A19. a) Prospective earth fault current and Prospective short circuit current
b) The higher of the two
Q20. State three locations in an electrical installation where phase sequence would need to be confirmed
A20. Origin of installation, At the distribution board, At end of final circuit supplying a motor
Well thats the first 20 questions and my fingers are abit sore now lol. My only problem with this course is that some of the questions are so ambiguous half the time I know the answer just cant understand what the question nis answering me. So please if any of my answers are wrong let me know
Thanks
r10ley
Q1. BS 7971 requires an inspection to be made on installed electrical equipment during the initial verification. State the three areas to be verified.
A1. .All electrical equipment and materials are of the correect type and comply with all relavent British Standards
.All part of the fixed installation are correctly selected and erected
.No parts of the fixed installation is visually damaged or otherwise defective
Q2. a) Two items of information regarding the protective device at the origin, to be obtained from the distribution network operator.
b) What the designer may take into account when determining maximum demand
A2. a) The rating of the device and its rated short circuit capacity
b) The full load of the installation with diversity applied
Q3. State one statutory and two non statutory publications which relate directly to the inspection and testing process
A3. Statutory - Electricity at work regulation, Non Statutory - BS7671 and Guidance note 3
Q4. A steel conduit and trunking installation has been erected and is to be inspected prior to the installation of cables. State three inspection items which will be checked using the sense of touch.
A4. No sharp edges, conduit is reamed and bushed
Trunking lids are secure
All conduit trucking and accessories are securely fixed
Q5. The electrical installation in a sandwich bar is to be inspected and tested in order for the owner to obtain a license from the local authority. State
a) the two parties with whom the inspector must discuss the requirements for the inspection and test
b) where the outcome of the discussion is to be recorded
A5. a) The local authority and the sandwich bar owner
b) On the periodic inspection report form under extent of installation inspected and limitations.
Q6. List three operational characteristics of a low resistance ohmmeter as identified in guidance not 3.
A6. .No load voltage between 4V and 24V
.Short circuit current not less than 200mA
.Test current a.c and d.c
Q7. a)State two reasons for the prescribed sequence of test prior to energising a new circuit.
b)State one test on an installation forming part of a TT system which may be carried out as either a live test or a dead test.
A7. a)To ensure that the polarity is correct and that no short circuits exist on the installation prior to energising it.
b) Resistance of the earth electrode (Ze)
Q8. State one method of verifying each of the following (each method must be different)
a)Continuity of a lighting circuit CPC
b)Continuity of a main protective bonding conductor 40m in length
c)Continuity of the earthing conductor
A8. a)R1 +R2 test
b)Wandering lead test
c) Ze test
Q9. A conductor of length 50m has a resistance of 2.3mohms/m. A second identical conductor is to be installed in parallel with this conductor. Determine the total resistance of these two conductors when connected in parallel. Show all calcs.
A9. Resistance of conductor = (2.3 x 50)/1000 = 0.115
1/RT = 1/R1 + 1/R2
1/RT = 1/0.115 +1/0.115
1/RT = 17.4
RT = 1/17.4
RT = 0.057 or 57mohms
Q10. State a)two factors which will reduce the insulation resistance of a new installation measured at the distribution board with all the circuits connected.
b)the voltage to be applied when testing the insulation resistance of a 400V ac circuit
A10. a) Number of circuit connected in parallel
b) Length of circuit (decrease when longer)
Q11. A circuit which includes surge protection devices is to be tested to determine insulation resistance. State
a)two methods recognised in BS7671 for safely testing this circuit
b)the minimum test voltage which can be applied
A11. a) Remove surge protection and link out or if not possible test with reduced test voltage
b)250V dc
Q12. An insulation resistance test is carried out on each of the following circuits. State the test voltage to be used in each case.
a)25V SELV lighting circuit
b)650V three-phase motor circuit
c) 110V reduced low voltage circuit
A12. a)250V DC
B)1000V DC
C)500V DC
Q13. State three special locations identified in BS7671 which are divided into zones
A13. Swimming pool, Area containing a bath or a shower, A sauna
Q14. State the appropriate IP protection to be provided for the
a)top surface of a readily accessible motor starter
b)front of a readily accessible distribution board
c)internal barrier within a consumer unit where the cover can be removed without the use of a tool or key
A14. a)IPXXD
b)IPXXB
c)IPXXB
Q15. A BS 1361 fuse is to be used to provide overcurrent and fault protection for a new circuit. State the effect on the operation of the fuse when the following conditions occur if the fuse was installed in the neutral conductor,
a)overload fault
b)earth fault
c)short circuit fault
A15. a)Fuse will operate however the supply will not be cut off
b) The fuse will not operate
c) The fuse will operate but the supply will not cut off
Q16. State a)The test instrument used to measure the earth electrode resistance for
i/ a generator
ii/ an installation protected by an RCD and forming part of a IT system
b)the number of readings to be taken for the test in a)i/ above.
A16. a) i/Earth electrode resistance tester
ii/Earth loop impedance tester
b) 3
Q17. State a)two methods by which the external earth fault loop impedance (Ze) may be determined
b)one method of determining Zs when direct measurement is not possible (Not Ze)
A17. a)Driect measurement and enquiry
b)Calculation Zs=Ze+(R1+R2)
Q18. State the maximum permitted time/current performance criteria for a 30mA BS EN 61009 RCBO when tested at
a)15mA
b)30mA
c)150mA
A18. a) No trip
b) 300 ms
c) 40 ms
Q19. a) List the two test measurements to be taken in order to determine PFC at the origin of a single phase electrical installation
b) State which of the measured values is to be recorded
A19. a) Prospective earth fault current and Prospective short circuit current
b) The higher of the two
Q20. State three locations in an electrical installation where phase sequence would need to be confirmed
A20. Origin of installation, At the distribution board, At end of final circuit supplying a motor
Well thats the first 20 questions and my fingers are abit sore now lol. My only problem with this course is that some of the questions are so ambiguous half the time I know the answer just cant understand what the question nis answering me. So please if any of my answers are wrong let me know
Thanks