2392 Question | on ElectriciansForums

Discuss 2392 Question in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Joined
May 20, 2009
Messages
241
Reaction score
33
Location
Minnions
When testing continuity of a ring final circuit wired with 2.5/1.5 PVC/PVC conductors using 'Method 1'. The value of R1 is 0.8ohm, what should be the approximate value of R2:

A: 1.20
B: 2.00
C: 1.34
D: 0.32
 
I know it probably doesn't matter in the context of the question but the end to end values of a ring circuit are known as r1 (line), rn (neutral) and r2 (cpc) (notice the small r).

You would expect R1 (big R) to equal r1 ÷ 4 and R1+R2 to equal (r1+r2) ÷ 4

Just something to remember for the future.
 
Upvote 0
I know it probably doesn't matter in the context of the question but the end to end values of a ring circuit are known as r1 (line), rn (neutral) and r2 (cpc) (notice the small r).

You would expect R1 (big R) to equal r1 ÷ 4 and R1+R2 to equal (r1+r2) ÷ 4

Just something to remember for the future.

Very good and relevant point JUD, i know this is 2392, but make that small mistake in the 2394 or 2395 and marks will be lost.

Cheers.........Howard
 
Upvote 0
R1 size / R2 size = 1.666666667
1.6666667 x 0.8 = 1.3333333

Should be C, 1.34

The answer is C.

I see now. R1 size as in diameter of cable 2.5mm, doh! So it'll be - 2.5/1.5 = 1.666666667

then like you say 1.666666667 x the R1 value 0.8 = 1.3333333

Great, althought would it be different for a radial? 0.5?
 
Upvote 0
radial would be R1+ R2 =answer

So In this book that I have it says

"A radial circuit is wired in 2.5mm2 phase and 1.5mm2 CPC. The test resistance of R1 + R2 is 0.37 ohm.

To calculate the resistance of the CPC on its own:

R2 = 0.37 x 2.5 / 2.5 + 1.5
R2 = 0.37 x 0.625 = 0.23 ohm

So using that with the original question I get:

R2 0.8 x 0.625 = 0.5 ?
 
Upvote 0
The original question gives you the value of R1 on it's own so R2 is worked out as follows

R2 = R1 x (2.5 ÷ 1.5 or 1.67)
R2 = 0.8 x 1.67
R2 = 1.34

The question in post #8 gives you the combined value of R1+R2 so

R1 = R1+R2 x 1.5 ÷ (1.5 + 2.5)
R1 = 0.37 x 1.5 ÷ (1.5 + 2.5)
R1 = 0.14

R2 = R1+R2 x 2.5 ÷ (2.5 + 1.5)
R2 = 0.37 x 2.5 ÷ (2.5 + 1.5)
R2 = 0.23

This is the same for a ring or a radial
 
Last edited by a moderator:
Upvote 0
I get R2 = 0.23125Ω, and R1 = 0.13875Ω.
Divide the value for R1+R2 by the combined CSAs.
Then multiply by the other CSA to the one you want to find the value for.
2.5 + 1.5 = 4.
0.37Ω / 4 = 0.0925.
R1 = 0.0925 x 1.5 = 0.13875.
R2 = 0.0925 x 2.5 = 0.23125.
 
Upvote 0
So In this book that I have it says

"A radial circuit is wired in 2.5mm2 phase and 1.5mm2 CPC. The test resistance of R1 + R2 is 0.37 ohm.

To calculate the resistance of the CPC on its own:

As tel. has stated, its quite straight forward

If R1 + R2 = 0.37 Ohm and R2 is 1.67 times greater than R1

then 2.67x = 0.37
x = 0.37 / 2.67
x (R1) = 0.13 Ohm
and
R2 = 1.67x * 0.13 = 0.23 ohms or 0.37 - 0.13 = 0.24 ohms

You can find the theoretical resistance of r1 and r2 if you get excited
 
Upvote 0
As tel. has stated, its quite straight forward

If R1 + R2 = 0.37 Ohm and R2 is 1.67 times greater than R1

then 2.67x = 0.37
x = 0.37 / 2.67
x (R1) = 0.13 Ohm
and
R2 = 1.67x * 0.13 = 0.23 ohms or 0.37 - 0.13 = 0.24 ohms

You can find the theoretical resistance of r1 and r2 if you get excited

Well explained. Simple solution that demystifies the problem.
 
Upvote 0

Reply to 2392 Question in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
414
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
He is after the four options for 1 and 2 of the multiple choice exam, probably optimistic someone will know this. Your question 3 in incomplete to...
Replies
2
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top