Question in 2395 past paper need help please.

if someone can show me how they worked this out

a circuit wired in 2.5mm/1.5mm twin with CPC sheathed copper cable has an r1 + r2 reading of 1.33 ohms, the value of r2 measured separately would be

1. 0.83
2.0.5
3.1.0
4.0.33

all in ohms

thanks
 
So just using the 1.67 to 2.67 ratio in the former equation multiplied by 6 and divided by 2 to give a fraction of 5 divided by 8 to use as a factor on the given value of resistance to resolve the answer.

Sorry... just being silly!
 
Because the earth is 1.5mm² and the line 2.5mm² the earth will have 1.67 times greater resistance than the line.

The total resistance is R1+R2, but because R2 will be 1.67 * R1 the total resistance will be 2.67 * R1 (1 R1 plus 1.67 R1).

So the resistance of the earth is the total resistance multiplied by (1.67 / 2.67) and this is equivalent to 5/8 (if you multiply both sides by 3).

Maths wise

R1 = R2 / 1.67
or
R2 = R1 * 1.67

Rt = R1 + R2

Substituting for R2
Rt = R1 + (1.67* R1)
Rt = 2.67 * R1

Since R1 = R2 / 1.67

Rt = 2.67 * (R2 / 1.67) = 2.67/1.67 * R2
So R2 = 1.67/2.67 * Rt
1.67 * 3 = 5
2.67 * 3 = 8

So R2 = 5/8 *Rt
 
Ignore my post number 5

If you cannot see where the 2.67 comes from by the use of post 8 then I am afraid I cannot assist.

total resistance is R1 + R2
R2 is 1.67 * R1 so you have

total resistance is R1 + (1.67 * R1)

therefore you have a single R1 plus 1.67 R1
1 + 1.67 = 2.67

so you have 2.67 R1
 

Reply to 2395 estimating r1 + r2 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
259
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
749
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
738

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
242
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top