@ Malcom,

The new GN3 gives three methods now, 1) the usual earth rod tester with spikes, 2) the newer 'stakeless' rod testers, and 3) the EFLI method.
The last method does not now give any reference to RCD's whatsoever.

I wouldn't use these for single point testing, but are fine where multiple rods are involved....
 
So glad you boys are having to look the TT question up. I totally blanked on it. Not having any idea you could do an efli test instead of thee usual dead test. I put test the rcd ifvit trips in time it proves your earthing but includes parallel paths, thought it was wrong, but better owt than nowt.!
 
So, with reference to the new GN3 and the removal of the RCD requirement, and the regs Malcom referred to, does this mean that we can now test all Earth rods by the EFLI method ?
 
So, with reference to the new GN3 and the removal of the RCD requirement, and the regs Malcom referred to, does this mean that we can now test all Earth rods by the EFLI method ?

To be absolutely honest, i was under the impression that's exactly what the vast majority of self employed electricians use, to measure earth rod resistances. As i say, what other method is there, if you don't own/possess a dedicated earth electrode tester?? lol!!
 
So glad you boys are having to look the TT question up. I totally blanked on it. Not having any idea you could do an efli test instead of thee usual dead test. I put test the rcd ifvit trips in time it proves your earthing but includes parallel paths, thought it was wrong, but better owt than nowt.!


Hi gesl,

You used to be able to use the EFLI method (as Widdler pointed out) where the install had RCD protection, which in practice meant almost all domestic and smaller commercial sites (except when Ra was at TN levels) where high EFLI meant this was the only practical way of achieving disconnection times.
You just did a normal Ze test with your MFT, and this gave you your Ra value, as E54 said, not many electricians these days have the earth rod testing kit except on the larger sites, and possibly those working for the utility companies and other specialist contractors.

It appears that the new GN3 has removed the RCD requirement, however I would imagine that the rod testing kit is still a requirement for the more specialised sites.
 
To be absolutely honest, i was under the impression that's exactly what the vast majority of self employed electricians use, to measure earth rod resistances. As i say, what other method is there, if you don't own/possess a dedicated earth electrode tester?? lol!!

I was going to say the same thing but didn't dare :lol:

On my 2395 I am sure i was taught that the EFLI was only valid if a RCD was present as accurancy was not so important in that situation but it does appear from the regs that this bit has been dropped now. To be fair the updated GN3 wasn't available when I did mine!

To the guys that found the 2395 harder than expected, don't panic! I felt the same after mine - from revising 2391 I thought I would be ok but found a number of questions I didn't get the point of until discussing them with colleagues afterwards. But I passed :)
 
I was going to say the same thing but didn't dare :lol:

On my 2395 I am sure i was taught that the EFLI was only valid if a RCD was present as accurancy was not so important in that situation but it does appear from the regs that this bit has been dropped now. To be fair the updated GN3 wasn't available when I did mine!

You put it clearer than I did lol, that is partly what I was trying to say in the previous post.

E54,
I have never (up to now) needed to test the earth mats/multiple rods on the larger industrial or commercial sites since being self employed (and doubt that I will), but if I did I would have probably either bought or hired the rod testing kit, and I suppose it would depend on the specs/standards of the job whether this is still a requirement or not.
 
I was going to say the same thing but didn't dare :lol:

On my 2395 I am sure i was taught that the EFLI was only valid if a RCD was present as accurancy was not so important in that situation but it does appear from the regs that this bit has been dropped now. To be fair the updated GN3 wasn't available when I did mine!

To the guys that found the 2395 harder than expected, don't panic! I felt the same after mine - from revising 2391 I thought I would be ok but found a number of questions I didn't get the point of until discussing them with colleagues afterwards. But I passed :)

Using an EFLI test to acquire the Ra value of a rod, is a reasonably accurate method of testing!!

Virtually ALL TT systems in the UK would require RCD protection, with such a high max requirements, let alone the lack of stability that's given to TT systems these days...
 
The only other one that I can think of at the moment was

Q.Under what conditions may you exclude the testing of continuity of ring final circuits.

Again in the cold light of day I have since found an answer of sorts in GN3 but as gesl says the 2391 past papers we were practicing on lead me to concentrate on certain questions that kept coming up such as earth fault paths, resistors in parrell etc and it caught me completely off guard.
 
It appears that the new GN3 has removed the RCD requirement, however I would imagine that the rod testing kit is still a requirement for the more specialised sites.

From what I can see there has never been a requirement to include a RCD in testing the Ze(Ra) of a TT installation

Earth electrode, clamp measurements and ELI testing are all still valid and do not require a RCD to be present. In fact RCDs are one hell of a hindrance and IMO you would test up stream or with the earthing conductor disconnected.

RCDs make allowances for a Ze (Ra) coupled with R1+R2 of the largest circuit when the required Zs for disconnection time is non compliant with table 41.1.

Having said that both Ia and IAN are valid (411.5.2)
 
From what I can see there has never been a requirement to include a RCD in testing the Ze(Ra) of a TT installation

Earth electrode, clamp measurements and ELI testing are all still valid and do not require a RCD to be present. In fact RCDs are one hell of a hindrance and IMO you would test up stream or with the earthing conductor disconnected.

Hi Ackbar,

That is basically what I said in some previous posts in this thread:

Hi E54,

When testing TT system Ze (Ra) I don't test through the RCD, as Widdler pointed out the reg said you could use the EFLI method where the installation was protected by an RCD, not that you tested through the RCD.​

The new GN3 gives three methods now, 1) the usual earth rod tester with spikes, 2) the newer 'stakeless' rod testers, and 3) the EFLI method.
The last method does not now give any reference to RCD's whatsoever.​


As Widdler pointed out, the 17th Ed pre Amd 1 and the previous GN3 does mention having an RCD present to be able to use the EFLI method.

The new GN3 has removed the references to RCD's altogether.

Cheers, S68
 
Last edited:
Hi Ackbar,

That is basically what I said in some previous posts in this thread:

As Widdler pointed out, the 17th Ed pre Amd 1 and the previous GN3 does mention having an RCD present to be able to use the EFLI method.

The new GN3 has removed the references to RCD's altogether.

Cheers, S68

I think it refers to Zs testing not earth electrode testing.

Since RCDs are mentioned in both GN3 17th ed (page 51) and 17th ed amd 1 ( page 53) when referring to Zs testing.

Moreoever, RCDs are mentioned when electrodes testing 17th ed (page 47) and amd 1 (page 51). But GN3 17th ed amd 1 removes the ambiguity that earth electrode testing should be tested through a RCD, which is a bit of a facility when you consider the rubbish being pumped along the supply cables and your tester is set to something in the order of mA......
 
Hi Ackbar,

The previous GN3 (P47) says:

Earth Electrode for RCD's

If the electrode is being used in conjunction with a residual current device the following method of test may be applied as an alternative to the earth electrode resistance test described above (refers to spike type testers), in these circumstances, where the electrical resistances to earth are relatively high and precision is not required, an EFLI tester may be used.

The new GN3 (p50) has removed the references to RCD's altogether

The new GN3 gives three methods now, 1) the usual earth rod tester with spikes, 2) the newer 'stakeless' rod testers, and 3) the EFLI method.
The last method does not now give any reference to RCD's whatsoever.​

This now appears to allow the use of EFLI testers whether an RCD is present or not.

In neither case does it mention testing through the RCD, which is what I said previously ie. you would test the rod as you would normally do a Ze test, and not through the RCD.
 
This now appears to allow the use of EFLI testers whether an RCD is present or not.

GN3 16th ed, 17th ed and 17th ed amd 1 recognize EFLI as one method of testing the earth electrode.

When GN3 was first introduced Circa 1992 RCDs were just finding prominence. So the standard methods of testing were propriety earth electrode testing, EFLI testing and Clamp testing.
There is nothing new here...
 
GN3 16th ed, 17th ed and 17th ed amd 1 recognize EFLI as one method of testing the earth electrode.

There is nothing new here...

I have the OSG 16th ed and the two 17th ed GN3 (I cannot find my 16th Ed GN3)

The 16th ed test (in the OSG) and the 17th Ed:2008 (GN3) both say you may use the EFLI method if the rod is used in conjunction with an RCD


The 17th ed amd 1 GN3, has now removed this RCD requirement. This is what is new :cheesy:

 
Last edited:

Reply to 2395 Last Night ? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
316
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
962

Similar threads

Oh I totally would have done there mate too. There were some fireworks near me that did usual fireworks for a bit then drones making all sorts...
Replies
6
Views
356
  • Question
I'll DM you.
    • Like
Replies
11
Views
980

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top