I'm doing my 2395 practical assessment this week and I'm looking through my condition report inspection schedule.

in the case I come up against a low ( < than 1 mohm ) value on mega ohms while completing a IR test which box in the inspection schedule should I code this fault struggling to find a box which relates to it.

thanks in advance
 
A low IR reading would not be noted in the schedule of inspections as it is not something for which you can inspect.
The low IR reading would show up in the schedule of test results as it is part of the electrical testing you do.
Then on the schedule of test results you can put a reference number relating to the observation you make and the coding you apply.
 

Reply to 2395 practical assessment in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Definitely, although most likely within the accessories. I've often found that once accessories are disconnected the cabling IR is fine. Sometimes...
Replies
19
Views
2K
Went into an MCCB, terminated very nicely thank you very much, however it was just me doing some training with crimping. 'introducing extra point...
Replies
11
Views
638

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top