J
juz571
Hi all, I am slowly working through my design to gain this qual, and have come up against a little teaser when starting my ring main design calcs. I have (at the moment) split the ring mains into 5 or 6 seperate ones, and they range in length from about 90M to 130M total length (including drops and return leg). The problem I have is when I do my grouping factors. I was going to run all circuits in a suspended trunking around the building and then take them in conduit down to their positions. Now, as soon as I put 20 (will be more at the origin) circuits in the grouping factor table, I instantly get a 0.38 multiplier, which takes the cable size over 4mm2 and stops me having a ring main. I know I can maybe change to tray and run the cables in a single layer, to increase the multiplier, but in reality with the amount of circuits involved it would take about a 3M tray! Almost all installs I do at work contain many more than 20 circuits, in a single trunking, and unless very long are usually designed at 2.5mm2. I am just wondering if I am missing anything here, or if anyone has any thoughts. Any help or ideas would be greatly appreciated. Thanks.