G

guest119

Seen an ammended control panel today sporting a bs 60898 DP type C 2 amp mcb controlling 24v dc.

Usually weidmuller etc din rail fuseblocks and links.

Something I am missing?

Boydy
 
AmazingKarnak.jpg


No, still can't see it.
 
Seen an ammended control panel today sporting a bs 60898 DP type C 2 amp mcb controlling 24v dc.

Usually weidmuller etc din rail fuseblocks and links.

Something I am missing?

Boydy


I can't see what your problem is or what your missing?? lol!! MCB's protecting DC circuits is perfectly acceptable, when they are designated suitable for DC protection by the manufacturer!!
BTW, the Schneider web page you linked too, is from they're USA site...
 
I can't see what your problem is or what your missing?? lol!! MCB's protecting DC circuits is perfectly acceptable, when they are designated suitable for DC protection by the manufacturer!!
BTW, the Schneider web page you linked too, is from they're USA site...
An understanding of the functioning of mcb's perhaps?
 
C60HB, C60HC and C60HD are suitable for 24v DC .....

The number of poles required on your DC breaker is determined by the type of DC system you have:-

1- one polarity of dc supply is earthed
2- center point of the dc supply is earthed
3- insulated systems

As already mentioned you linked to a mcb designed to comply to UL requirements as areas including USA have differing regulations from us and the mcb's we use would not comply in their control systems..hence you have a differing dc rating and you have got yourself confused.
 
Hi,

Schneider MCB's are acceptable for DC provided you follow their guidance, they generally have to be down rated though. In their catalogue they have a page on 'DC operation of Miniature Circuit Breakers'.

Regards.
 
Apart from Phil can none of you realise the significance of my asking what size of the transformer feeding the rectifier was? Hint PFC!

Because DC doesn’t go through a neutral transition 100 times per second it is harder to break. To sustain an arc requires energy. You are not going to get that energy in a control panel due to the impedance of the control transformer feeding the rectifier! The energy let through is going to be minuscule!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
24 volt dc
Prefix
N/A
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
16

Advert

Thread statistics

Created
guest119,
Last reply from
guest119,
Replies
16
Views
4,011

Advert

Back
Top