TestEngineer

I will make an installation for fire alarm system (detectors 240V supply with interlink between of each one) using single wires or pvc cable enclosure in pvc conduit or pvc trucking.The detectors have the symbol of double insulation with out any point for earth terminal and my question is if there is any requirement (17th Edition IEE) to pass cpc conductor with the live conductors as escort?
 
And now I've had a couple of minutes to look it up:

Reg 411.3.1.1 of the BGB:

A Circuit Protective Conductor shall be run to and terminated at each point of wiring and at each accessory except a lampholder having no exposed-conductive-parts and suspended from such a point.
 

Reply to 240V & CPC conductor in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
275
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
773
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
779

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top