J

Jmagee

Hi folks new to this but have a question . What are the circumstances that have to be met to fit a 240v fan in zone 1 . I have read that it's acceptable if the fan is ipx4 rated and is on a rcd. I've read that if the manufacturer states the fan is suitable for zone 1 and rcd protected then it is also fine . I have read that it has to be rear cable entry (hidden) with any double insulated fan on rcd then it's also fine . Then on the other hand I have heard 240v fan in zone 1 is a no-no . Does anyone know it would be really helpful
 
Well, the manufacturers instructions are statutory, so follow them. What type of fan is it? Have you provided a fan isolator? Does the MI require it to be down rated to a 3 amp fuse?

Jay
 
A 230V ventilation fan in Zone 1 must be suitable for that zone according to the manufacturers, it must have a minimum degree of protection of IPX4, (if there is the likelihood of high pressure water sprays such as jet washing then the minimum protection would need to be IPX5), no external switch is permitted in the zone but if there is an internal switch and the manufacturer states it is suitable for zone 1 then this is acceptable.
All LV circuits in a bathroom must be protected by a 30mA RCD and this includes the fan.
If the fan meets these requirements then it can be installed in zone 1.
Obviously all general rules apply as well so that it must be suitable for the external influences encountered and suitably protected against overcurrent, etc, etc.
 
I recently had this scenario on a eicr where the fan was sited 600mm up from the top of a bath. I was ready to code it a c2 but looked at the zones and ended up not coding it. Certainly wouldn't be me putting a fan there!!


Sent from my iPhone using Tapatalk
 
But BS7671 ISN'T STATUTORY!!

If you don't follow the MI, then you could be putting people/property at risk and it will void the warranty (unless agreed with the manufacturer).

What about blindly following MIs that could potentially cause danger or are non compliant with the regs ? I've lost count of the times I've come across (and ignored) those.
 
Last edited:
What about blindly following MIs that could potentially cause danger or are non compliant with the regs ? I've lost count of the times I've come across those.

I was speaking to a lad the other week that had to fit a CO2 detector 500mm from the boiler, as per the spec. But the MI's stated at least 1000mm away. He raised this concern with the site foreman. What happens if there was a fault with the boiler and the alarm doesn't go off? Who's gets the blame? Obviously you would try and satisfy all regulations and MI's but I would try and follow the Mi's if there was a conflict. They have tested their equipment and they know how and where it should be installed. saying that, some equipment and the MI's don't conform to British standards anyway!! So you would use other regs for info.

I don't blindly follow them, I still use my own judgement and interpretations for each install as they will all be different.
 
Ok, so I have had a look and apart form the odd mention in the PUWER and Electrical safety regs, it doesn't actually state they are mandatory, so I will hold my hands up there and say, every day is a school day. This is what I was taught years ago and have never really thought about it since.

But I still think as electricians we need to be making the judgement on whether the equipment is fit for the environment, given all the relevant info in the regs and MI's. If for example the MI's state that the fan should not be fitted in any zone but the BS7671 says it can be, I would always follow the MI's because f anything goes wrong, I think these would make a better case in court.
 
To be fair to jay, take the post on SY cable, Eland say it is not suitable for outside use . Would you follow , or ignore it?
 
I was speaking to a lad the other week that had to fit a CO2 detector 500mm from the boiler, as per the spec. But the MI's stated at least 1000mm away.

I presume you mean carbon monoxide /CO) a opposed to carbon dioxide (CO2), but how do you know that it will operate correctly/effectively at 500mm? I believe 1 to 3 metres from the appliance in a horizontal plane is suggested.
 

Reply to 240v Fan in zone 1 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
307
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
828
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
929

Similar threads

He said something about a fused something as the lights hardly take anything .. I told him was mostly cordless tools so just chargers ..told him...
Replies
11
Views
620
In July I moved into my new home with Schluter DITRA heated floors in the bathroom. The floor quit working in December, and my GC and a rep from...
Replies
0
Views
669

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top