i was asked to check why a tank heater was not working properly today an came across something im pretty sure is wrong. but was wondering if any of you had any thoughts on
the element 240v rated was connected to two phases (one at each teminal ,no neutral) via seperate breakers, i dont know how long this had been the case .its now isolated till i fathom it out:banghead:
is there any reason why somone would do this??
its puzzling me?
the element seems to have good continuity and is showing 250M ohms to the metal casing
 
It’s OK showing the IR reading, CR would be more useful. If the element has survived then it’s a simple enough job to swap one line to the neutral.

PS. You sure it’s a 230V element? I’ve fitted plenty of 433V immersion heaters.
 
i have re jigged the wiring yesterday to make it 240v so now the cal controller is switching on an off as it should.
CR?? continunity readiing?
i cant get these readings at the mo as the test rig is running and the terminals / rating cap are right next to a spinning belt.
just puzzled me as to the thought process of whoever put it in
i cant do any further investigations till the rig stops.
 
just puzzled me as to the thought process of whoever put it in
You can run element tubes on voltages other that those stamped on them. You need to calculate the tube surface temperature which depends on several factors such as the heat density of the element, the tube surface area, the material the tube is made from, the fluid or medium the element is immersed in etc etc. The fact that your element is still in tact after prolonged running on 400v suggests someone may have done these calculations and specified 400v as the design voltage. By reducing this voltage you may be impairing the functionality of the system as a whole.
 
Ive checked the other test rigs and this is the only one running 2 phases thru the elements.
The previous maintenance sparky had a rep for being a bit rough.
The elements are heating 15w40 diesel oil.
This post was more of a wtf ?moment , so i was kinda passing it out to the collective minds to see what they thought.
Once this rig finishes its tests ill have a chance to see what the details are.
More news at 11
 
Last edited:
Just out of curiosity,were the "two separate breakers" linked? and did you identify the fault? :wacko:
 
installed 2 new 240v heaters and re jigged the wiring:party:
the old ones when taken out and checked more thoroughly were bad they were breaking down)so not working properly.it took a while for down time to remove the tanks and heaters to allow proper testing servicing to be carried
out
.
 

Reply to 240v heating element connected through 2 phases? in the Talk Electrician area at ElectriciansForums.net

Similar Threads

Thanks all for the suggestions! Customer doesn't store anything else in the cupboard with the tank, not even towels or sheets. Heatrae stat is...
Replies
11
Views
920
  • Question
That is a possibility, but seems a bit excessive. If there is an easier way to do it, I will.
Replies
7
Views
1K
Your kWh figures are giving you consumption averaged over each hour period, but don't give an indication of total instantaneous current. To try...
Replies
9
Views
901
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
670
I fitted a Mem MR30 Pod and MCB, about £75 for both.
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks