Dear all,
I work for an exhibition company and manage the technical side of things there.
As a new feature for a booth concept we need to setup some 24V RGB LEDs to backlight some stretched fabric.
The PSU that I am using is ACDC 24V 13A.
The RGB controller unit that I am using allows 3x3A circuits before having to use a repeater coupled with another ACDC PSU of suitable rating.
The RGB ribbon uses 14.4W per meter, 5m = 72W/24V = 3A per 5m roll (We intended on using the full capacity of the controller).
Basically I am trying to source suitable 4 core cable online however most data cable rating is a low amperage and the draw on our setup will be around 10A.
On TLC I have found 1.5mm 4 core flex 16A used for central heating systems etc.. They also have a 1.0mm version but is only rated at 10A.
I'm worried about using the 1.0mm just incase anything went wrong in the circuit, the cable would be 3A under the PSU rating (Even though the PSU should only be sending out 9A to the controller)
Am I right in thinking that even though it is only 24V the potential draw from the LED ribbon through the controller will be 9A max +/- 5% from the PSU that can allow a total of 13A +/- 5%.
Should I go with the 1.5mm cable so the wiring is rated slightly higher than everything else?
Should I just go with the higher rated ACDC 24V 13A PSU for tolerance or should I just use the ACDC 24V 10A PSU and use the 10A Cable?
Thanks for your help (Sorry if this does't make sense.. )
I work for an exhibition company and manage the technical side of things there.
As a new feature for a booth concept we need to setup some 24V RGB LEDs to backlight some stretched fabric.
The PSU that I am using is ACDC 24V 13A.
The RGB controller unit that I am using allows 3x3A circuits before having to use a repeater coupled with another ACDC PSU of suitable rating.
The RGB ribbon uses 14.4W per meter, 5m = 72W/24V = 3A per 5m roll (We intended on using the full capacity of the controller).
Basically I am trying to source suitable 4 core cable online however most data cable rating is a low amperage and the draw on our setup will be around 10A.
On TLC I have found 1.5mm 4 core flex 16A used for central heating systems etc.. They also have a 1.0mm version but is only rated at 10A.
I'm worried about using the 1.0mm just incase anything went wrong in the circuit, the cable would be 3A under the PSU rating (Even though the PSU should only be sending out 9A to the controller)
Am I right in thinking that even though it is only 24V the potential draw from the LED ribbon through the controller will be 9A max +/- 5% from the PSU that can allow a total of 13A +/- 5%.
Should I go with the 1.5mm cable so the wiring is rated slightly higher than everything else?
Should I just go with the higher rated ACDC 24V 13A PSU for tolerance or should I just use the ACDC 24V 10A PSU and use the 10A Cable?
Thanks for your help (Sorry if this does't make sense.. )
Attachments
-