We have been supplied with a machine that has a 24vdc power cable running through it. It looks like a 2.5mm cable. This is backed up by a 20A fuse in the machine control panel. At various points along its length there is a moulded "junction" where a much smaller cable (maybe 0.25mm ?) "tee's" off this main cable to plug in to some powered conveyor rollers.

My question is this ....

How many regulations is this breaking ?

Now, the rollers are internally fused, so we are only talking about protecting the 0.25mm cable ? A 20A fuse will obviously not provide adequate protection for this cable but it is very short and the risk of damage on this internally wired machine is negligable.

Any advice will be most appreciated.

Regards,

Mark.
 
How is the dc created is it through a basic transformer with rectification or do you have a d.c. power supply fitted as these tend to monitor for overload and short circuit protection etc and with respect the extra low voltages your dealing with what are the risks if any if the cable did get damaged?

In respect if you spur off a ring main in a house then this cable is to the spur is in effect over-rated by the 32amp front end fuse and this does leave potential for overload although 2 x13amp load would need to be plugged on it for a long period to effect this cable.
 
Last edited:
Hi darkwood,

The dc is from a power supply, but I have read other posts that say that these things are not that good with short circuit faults as they may just reduce the voltage to limit the current. With it only being a short length of cable, resistance would be at a minimum. So I = V / R which could melt things couldn't it ?

Regards,

Mark.
 
I assume if it did short circuit even if it reduced voltage then the fact the machine had stalled might interupt the control circuit anyway cutting the power but without the wiring plans its hard to say, i really dont consider this an issue due to the nature of the voltage and control system, and dont be mislead by the small cable they can be deceptive in their size if the insulation is only rated for extra low voltage, where the supply ribbon will be 240rated as it runs along side other voltage at some point in its length.
 
I agree with the original poster. There may be current limit within the power supply, but 0.25mm cable is rated around 1.4A so even if the voltage and current cut back in the event of a short, it could still be high enough to melt the cable.

I have seen this happen with a proxy fed via a 3 core 0.25 cable that sustaied damage causing a short circuit current to melt all its insulation.

If I was designing a control circuit, I would feed all proxys, photo-cells etc via a 2A fuse or breaker.
 

Reply to 24vdc machine wiring question in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

Click grid pro is by far the easiest one I've fitted. Schneider by far the worst
Replies
13
Views
4K
That makes sense. Adding unnecessary complexity.
    • Optimistic
    • Dislike
    • Creative
Replies
20
Views
3K
Perfect!! Thanks a lot gents. You've been massive help this last day 😁
2
Replies
43
Views
5K
Posted this to the DIY section since I'm not a business or employee in this matter but it feels more appropriate (and might actually get...
Replies
0
Views
1K
  • Locked
  • Solved
Therein lies the problem. I see no merit in further circular debate, so will bow out of this discussion.
    • Like
2 3
Replies
55
Views
7K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks