During an EICR i have found from the ryefield to each cut out wired in 25mm tails .
one of which is used a CNE conductor which is then split in the cut out housing to form a usual PME supply TNC-S.
i guess this was done by DNO or BNO .
is this safe and acceptable ?
[ElectriciansForums.net] 25 mm tails as a CNE conductor
Technically it can be argued as outside the scope of BS7671 as a BNO is deemed 'public supply', it's what's Right of the meter that matters.
Reply to 25 mm tails as a CNE conductor in the UK Electrical Forum area at ElectriciansForums.net
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...