It has an earthed sheath.
Mmm, not convinced.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss 25mm split con sub main eicr code? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
It has an earthed sheath.
So was twin and earthAt one time split concentric was deemed suitable for being in a wall without additional rcd protection but was removed in the one of the amendments to the 16th Ed.
Never realised that, not heard that.So was twin and earth
Always willing to pass on my knowledge to those who need itNever realised that, not heard that.
The requirement to provide RCD protection for cables concealed in walls, was introduced in the 17th.At one time split concentric was deemed suitable for being in a wall without additional rcd protection but was removed in the one of the amendments to the 16th Ed.
The split concentric I’ve used does.Not fully encasing the cable it doesn’t.
This will not comply with 522.6.204 indent (i )
Split con does not incorporate an earthed metallic covering which actually covers the entire cable
Quite correct error on my part. Nevertheless concentric was but no longer is suitable no matter it's construction.The requirement to provide RCD protection for cables concealed in walls, was introduced in the 17th.
So nothing was removed in the 16th.
No longer suitable for use in a domestic installation, or no longer suitable for use without RCD protection?Quite correct error on my part. Nevertheless concentric was but no longer is suitable no matter it's construction.
The split concentric I’ve used does.
One half is neutral, the other half earth.
No gaps.
In the UK, the neutral is generally earthed at source, which is why ESQCR allows split con to be buried in the ground.Exactly, the live conductors are not fully surrounded by earthed metal, neutral conductors are classed as live conductors.
Also split con isn't normally half and half, it's normally at least 2 thirds neutral.
As the regulation I posted states, it has to have an earthed metallic covering that completely encases the conductors, split con does not therefore unacceptable to be used for the purpose of burying in the wall without rcd protection , mechanical protection etcIn the UK, the neutral is generally earthed at source, which is why ESQCR allows split con to be buried in the ground.
In the UK, the neutral is generally earthed at source, which is why ESQCR allows split con to be buried in the ground.