hello guys i overheard a conversation last week about a supply to an outbuilding which will comprise of: 45A Shower, 32A Ring Final and 6A lighting. Total demand = 83A.

outbuilding is 28Mtrs from main house and will have no extraneous conductive parts as the water feed will be plastic.

now the spark was saying that a 25mm SWA buried in the ground will need to be run and can use the house main earth.

whats your thoughts on this guys??

regards
 
10mm is well adequate. the guy is talking through his arse. has he not heard of diversity?
 
25mm swa seems abit over the top to me. Doing a rough calc, 83A x 0.4 = 33.2A. Do some calcs and you will know what size cable you need.
Although I useally take out the biggest mcb, then add the rest, divide by 4 then add the biggest back for your total. This gives a slightly higher demand but still no need for the 25mm swa.lol
 
sorry, jay. you need to allow 45A for the shower, the 0.4 of the rest. that equates to around 60A.
 
then again that shower may not pull over 40A . manufacturers are overly optimistic with their figures.
 
I wonder which is the right way of working out demand?? I do the same by taking away the biggest mcb and adding it back to the total but I was tought to divide by 4. I know alot of lads multiply by 0.4. I suppose doing it the multiply by 0.4 way will give you a slightly higher demand and air on the side of caution!!
 
Funny how the question is always asked in the 2[SUP]nd[/SUP] inst. It’s never I think it should be what ever, but my friend thinks it should be……….

Funny old world. Or am I a cynic?
 
a lot of confusion arises over the fact that while a MCB may be 32A for a socket circuit, say, the actual load of the circuit may never get above 20A, sometimes even a lot less if it's not a kitchen RFC.
 
too late for calculations Tony!! Saturday night is beer time! lol

with this sort of attitude its no wonder people are put off making a post!!
 
its not a kitchen, will be a small gym comprising treadmill and rower. with shower.

i have been doing the comms cabling and just overheard this conversation.
 

Reply to 25mm SWA!! in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
348
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
888
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

totally agree
Replies
12
Views
1K
Sounds more positive.
Replies
8
Views
622

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top