2700w oven on plug & socket | on ElectriciansForums
Discuss 2700w oven on plug & socket in the Australia area at ElectriciansForums.net
solo2771
Hi I was at a clients house yesterday fitting a 17th edition board and found his 2700w oven is just plugged into the ring final circuit.
Am I right in believing it should have its own circuit, at the moment it is just the oven thats electric but if an electric cooker was to be fitted it would be well too much for the circuit even taking diversity into account.
Paul
Hi
We put all single ovens installed in a kitchen into a 13amp plugtop it's just an appliance like the kettle? and at 2.7kw is only drawing 10amps of the kitchen ring.
However if this oven is changed to a double oven at a laterdate a 6mm radial would be required of course?
as the KW rating goes up to over 7kw
It would make sense to run radials for all appliances but who is going to pay for it??
If there is a CCU present in the kitchen I fit a 13amp socket to the elephants trunk outlet which allows the single oven to be fused correctly and isolated from above worktop.
Check the manufactures info, fitted one the other day, it was rated around 2400w the manufacture requested that it be put on a min 15A and max 20A over current protective device, this rules out plug and socket, we down rated the 32A cooker circuit MCB to a 20A
Reply to 2700w oven on plug & socket in the Australia area at ElectriciansForums.net
Thank you for fast response. The reason I asked is because I had read elsewhere online: "Electric ovens have a wattage rating that tells you how...
There is no reason for an item of fixed equipment to be on its own dedicated circuit just because it is fixed equipment. There may be other...
loz2754
L