Just been asked to have a look at repairing an action that was on a PIR. It appears that there are 3 wires (from the socket 'ring') going in to the mcb together with 3 neutrals and 3 earths.
A quick confirmation indicates that and pairing of the 3 is continuous. 2 rings from 3 wires? (house seems to be wired in T&E plus singles - live and neutral are 2.5mm with a 1.5mm cpc)
I guess this is possible if 1 wire started say the upstairs ring and the other the downstairs ring and the return from both rings then ended up in the same socket before finally coming in to the consumer unit.
Does this mean that there is the possibility that one of the legs can be overloaded (as it would be if it was a radial off a 32A mcb?
Wondering if I need to recommend that the mcb is changed to a 20A until I can investigate further and trace each each cable?
A quick confirmation indicates that and pairing of the 3 is continuous. 2 rings from 3 wires? (house seems to be wired in T&E plus singles - live and neutral are 2.5mm with a 1.5mm cpc)
I guess this is possible if 1 wire started say the upstairs ring and the other the downstairs ring and the return from both rings then ended up in the same socket before finally coming in to the consumer unit.
Does this mean that there is the possibility that one of the legs can be overloaded (as it would be if it was a radial off a 32A mcb?
Wondering if I need to recommend that the mcb is changed to a 20A until I can investigate further and trace each each cable?