Hi All,
First thread in ages.
Recently went to a a pub to carry out some origin tests before they begin a total refurb.
It used to be a 3-PH supply / metering but they are only using 1-PH (red) with single PH metering.
I opened the service head to discover a core cable swa cable......
BUT they had used 2/3 of the armour as N and the rest of it earth-clamped with separate cable joining it to the Neutral.
So - on the outside it appeared to be TN-S but they made it a Temp TNCS.
N-CPC voltage at a DB near the supply intake indicating 230V!
Are DNO allowed to do this??
Customer advised that they had applied for a 3-PH supply, they only have 3 cores so I assume a new supply cable will have to be run TP&N and armour as CPC.
Any thoughts . comments appreciated.