SparkTech

Hi All,

First thread in ages.

Recently went to a a pub to carry out some origin tests before they begin a total refurb.

It used to be a 3-PH supply / metering but they are only using 1-PH (red) with single PH metering.

I opened the service head to discover a core cable swa cable......

BUT they had used 2/3 of the armour as N and the rest of it earth-clamped with separate cable joining it to the Neutral.

So - on the outside it appeared to be TN-S but they made it a Temp TNCS.

N-CPC voltage at a DB near the supply intake indicating 230V!

Are DNO allowed to do this??

Customer advised that they had applied for a 3-PH supply, they only have 3 cores so I assume a new supply cable will have to be run TP&N and armour as CPC.

Any thoughts . comments appreciated.

Regards
 
Hello, it was defo a swa cable and not a split consentric cable?? could look similar but are different.

(don't want to sound patronising but recently used some split con cable myself and tought then how similar it looked to swa)

Ross.
 

Reply to 3 core SWA supply with armour as N & CPC in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
787
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
810

Similar threads

I hate it when a shed is TTd, why can they not be extended from the tn system? popcorn ready
Replies
7
Views
668
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top