3 core t+e giving 45 volts when off | on ElectriciansForums

Discuss 3 core t+e giving 45 volts when off in the The Welcome Forum area at ElectriciansForums.net

mick b

-
Joined
Sep 8, 2013
Messages
20
Reaction score
5
Location
bolton
I have a 3 core t+e on a 2 way switch and when it is turned off there is still 45 volts at the light. I have stripped this down to a 1 way switch and the voltage disappears. I then meggered the 3 core and it is clear. There is continuity through the conductors and no obvious fault with the cable. The earth is connected but when I put the cable back on it goes to 45 volts again. Any ideas on induced voltages on 3 core cable.
Many thanks
 
If you do the same test with a real mans voltmeter ie one with a needle instead of a digital display I bet there's no significant voltage
images.jpeg

There's lots of threads around about the ghost or phantom voltages being a problem with the high input impedance of digital testers.
 
Any ideas on induced voltages on 3 core cable.

It's not induced. Copper is non-ferrous remember, you can't induce voltage copper to copper. The problem you have is capacative coupling, it is a phantom voltage and is harmless. Use an analogue multimeter and it won't register.

The most likely cause for this 'problem' for want of a better word, is degraded insulation.
 
Yes you can, induction occurs in any conductor if it moves through a magnetic field, or if an alternating magnetic field crosses a conductor.

You can't create a substantial magnetic field with a non ferrous material. Think! A ferrous material is needed to focus the induced magnetic force from one conductor to another :)

To induce a current in a copper conductor you need; alternating current --> copper --> ferrous material --> copper

If you want to induce measurable current from copper to copper, you would need miles and miles and miles of conductor with a gap between them so small it would be almost invisible to the eye! Even then you'd be talking microamps!

When I say you 'can't', what I really mean is that it's really really hard!
 
Last edited:
I've developed a high impedance to these questions now, that's why I don't respond to them anymore.
I might give a false answer.
The frequency of this particular question does point to an across the board lack of understanding in this particular area. It's obviously something that's not being covered properly in the training and I'm not convinced it's just the limited scope training that's at fault here.
 

Reply to 3 core t+e giving 45 volts when off in the The Welcome Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
771

Similar threads

  • Question
I think a 3 legged breakout boot would be your best bet in the circumstances.
Replies
3
Views
593
davesparks
D
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top