swifters

Why on a 3 phase supply do you only get a choice of 100amp/125amp or 250amp main switches? The basic domestic main switches are normally 100amp. I would have thought that with the added voltage, that there is a greater potential amperage? Granted resistance will be reduced with the 3 phases but is each phase not protected by a 100amp main fuse? 3 x 100amp being 300amps? Why is it that 125amp 3 phase main switches seem to be the norm?
 
In the example you posted above re:100A X 3 does not equal 300 A, it equals a 100A per phase.

It could be partly due to the manufacturers rationalising their ranges, and partly due to the need of a greater Icu (kA rating).
 
In the example you posted above re:100A X 3 does not equal 300 A, it equals a 100A per phase.

It could be partly due to the manufacturers rationalising their ranges, and partly due to the need of a greater Icu (kA rating).

I'm pretty sure the last job I saw with a 3 phase installation had 3 x 100A fuses. Surely if each phase is drawing 100amp (simultaneously; unlikely I know) then the 100amp main switch would not switch the power off? Would it not break?
 
I'm pretty sure the last job I saw with a 3 phase installation had 3 x 100A fuses. Surely if each phase is drawing 100amp (simultaneously; unlikely I know) then the 100amp main switch would not switch the power off? Would it not break?

You are correct wrt having 3 fuses, but they are on separate phases, the switch has 3 poles = 100A per phase in the example you are using.
 
I'm pretty sure the last job I saw with a 3 phase installation had 3 x 100A fuses. Surely if each phase is drawing 100amp (simultaneously; unlikely I know) then the 100amp main switch would not switch the power off? Would it not break?
No main switch would switch the power off due to overcurrent. The fuses are there to protect for over current. A main switch is exactly that a switch.
 
No main switch would switch the power off due to overcurrent. The fuses are there to protect for over current. A main switch is exactly that a switch.

Yes, so if you wanted to switch the power off yourself whilst everything was on then perhaps the main switch would not work? If each pole is capable of switching off 100amps then I suppose no worries? I know an electrician would know that you should switch off the MCB's/RCBO's before switching off the main switch but a layperson wouldn't. They would just flick the main switch, but I suppose the switch is in effect rated at 300amp's in total?
 
A 100A 3PTP isolater has 3 contacts rated at 100A - it has a physical size appropriate for the size of cable needed for 100A supply. Once above this then say a 250A isolater can be used for anything up to 250A, it will have a bigger physical size to accommodate the larger cables from anything around 25sqmm to 95sqmm odd.
Point is that as long as the isolater is at least as big as the upstream protection, no problems
 
No main switch would switch the power off due to overcurrent. The fuses are there to protect for over current. A main switch is exactly that a switch.


Unless of course the main switch is a MCCB!!

Anything larger than 250A on a typical 3 phase DB would be provided by a MCCB in most instances. Though i have seen more than a few German panels with 400A isolator switches
 
Last edited by a moderator:
Swifters,
Ah! I see what you are getting at, the isolator type you are asking about is usually an off load switch, like you say they are meant to be operated/switched off load (MCB's etc. switched off first), but I don't think the makers uprate them to take this into account, as they are still off load devices.
 
Swifters, All Switch Disconnectors must be compliant with the "parent type approval" IEC 69947-2 as well as various individual type approvals from the IEC, and as such they must be able to safely switch the full designed load of the disconnector (I think the requirement is that it must safely switch 150% of the designed load.

Here is some information related to a Merlin-Gerin (Schnieder) Switch Disconnector for one of their TPN panels.


  • Rating:20 to 125 A
  • Compliance with standards: EN 60669-1, IEC 669-1 for I 20 to 63 A; IEC 947-3 for I 40 to 125 A
  • Suitable for isolation in accordance with industrial standards: IEC 60947-2
  • DC application
  • Short-circuit withstand:20 x In for 1 s
  • Number of operating cycles:200 000 for I 20 and 32 A; 50 000 for I 40 to 125 A

So whilst it is advised that all loads should be disconnected prior to switching a main isolator/disconnector, they are actually designed to be capable of doing so.
 
Swifters, All Switch Disconnectors must be compliant with the "parent type approval" IEC 69947-2 as well as various individual type approvals from the IEC, and as such they must be able to safely switch the full designed load of the disconnector (I think the requirement is that it must safely switch 150% of the designed load.

Here is some information related to a Merlin-Gerin (Schnieder) Switch Disconnector for one of their TPN panels.


  • Rating:20 to 125 A
  • Compliance with standards: EN 60669-1, IEC 669-1 for I 20 to 63 A; IEC 947-3 for I 40 to 125 A
  • Suitable for isolation in accordance with industrial standards: IEC 60947-2
  • DC application
  • Short-circuit withstand:20 x In for 1 s
  • Number of operating cycles:200 000 for I 20 and 32 A; 50 000 for I 40 to 125 A

So whilst it is advised that all loads should be disconnected prior to switching a main isolator/disconnector, they are actually designed to be capable of doing so.

So in laymans terms it can knacker the switch if you keep turning it on and off under a heavy load.
 
With the likes of Merlin-Gerin (Schnieder), ABB, Seimens and the like, that's why you pay the big money. They are capable of disconnection under load. That's not to say you make a habit of doing so....
 
An isolator is just that, it isolates and isn’t designed to break load.

As E54 has said, you need a load break switch which bumps the price up.
 

Reply to 3 phase 125amp or 250amp main switch in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
259
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
742
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
730

Similar threads

When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
3K
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
986

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top