3 phase cable sizing | on ElectriciansForums
Discuss 3 phase cable sizing in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi Guys,
Little help please.Ive got to install a 3phase mortar silo. Information i have been given.
Requires a 16a 5 pin socket outlet (neutral and earth)
100m cable run
Max load 5KW
30ma RCD protected
Assuming c or d type
Its beeen a long time since ive dealt with 3 phase. could someone walk me through this?
Dont mean to sound thick but ive got total head block right now!!
Cheers
you need to find out the actual current per phase that the motor draws before you can calculate cable size. work your current out from the 5kW over 3 phases and go from there.
A couple of formulae that might help
Iz ≥ In ≥ Ib
It ≥ I2 / Ca x Ci x Cg x Cc
Iz = It x Ca x Cg x Ci x Cc
VD = (mV/A/m) x L x Ib / 1000
Reply to 3 phase cable sizing in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net