My sparky advised going off the busbar and I can't find the appropriate hardware - (mcb without switch / protection)
im I buying all the materials for him to install. I was unsure of his advice.
Piggy backing submains of existing 125amp distribution board as you explain in your opening post is poor design and will have drawbacks, if you are really stuck for any alternative then I would suggest fitting a 200amp busbar chamber to the wall and the supply feeding your existing distribution board is removed and fed into an Isolator which then feeds this new busbar chamber. From there you fit 3 outgoing sw/f isolators :-
1 - feeds existing board
2 - feeds sub-mains one
3 - feeda sub-mains two
This all has to be designed on site and it will need to be confirmed that the existing feed to your existing board has the capacity for the extra submains.
Voltage drop will also need to be calculated all the way back to the origin of your supply to the end of the sub mains you propose.
If you are advised to run the submains off mcb's in the existing board then this would be poor advice as it is poor design and a fault in you new submain circuits may equally take out the submain mcb thus losing all the power to all submain circuits as oppose to just the circuit at fault.
It would be almost impossible to design or advice you over a chit chat on a forum and I would strongly advise you get qoutes and designs from 3 or 4 recognised registered companies... this is not a job for a mate you know down the pub unless they are well seasoned and competent, its also not a job for anyone who only has experience in domestic.
We try our best to advice but sometimes its just not possible without seeing the installation and the proposed submains... your profile says farm and if this is correct then extra measures of safety need to be incorporated into the design so how ever tempting it maybe - don't cut corners (just a word of advise and I'm not suggesting you would cut corners).
You say you are running motors of the submains... this adds a complexity to the design, if they are small <5.5Kw then not too much of a worry but if we have larger motors then start up current will need to be calculated to ensure any upstream device including the front end for the existing cable will not trip out.